Power fed light switch and all lights test great, as soon as we put the dimmer switches in the Hager rcbo won’t trip, any ideas please
 
Hager ADA 306g 6amp rcbo the 4 gang dimmer are for led lights
 
Nothing obvious stands out to my mind, although my knowledge is less than comprehensive.
 
Are you sure it was tripping before installation of dimmers? Sorry, have to ask.
Could also be coincidence it has chosen this point in time to break.
 
How are you testing the RCBO trip
 
Are you sure it was tripping before installation of dimmers? Sorry, have to ask.
Could also be coincidence it has chosen this point in time to break.
Hi
Yes from each light fitting and again after taking dimmers out
 
Just a thought, I worked for a long time as a spark and AV engineer in the entertainment industry and some of the dimmers for LED stage lighting in that sector that I came across had fully isolated outputs. I haven't come across that in a domestic install personally though, but could it be????
 
depends what part of the cycle you are testing.
some dimmers are leading edge and some are trailing edge.
have you tried testing RCD on both positive and negative cycles?
most hager RCBO will trip within 1 cycle (20ms) regardless of testing at 0deg or 180deg.
 
depends what part of the cycle you are testing.
some dimmers are leading edge and some are trailing edge.
have you tried testing RCD on both positive and negative cycles?
most hager RCBO will trip within 1 cycle (20ms) regardless of testing at 0deg or 180deg.
Yes have tested on both cycles.
 
Wait, are you connecting your RCD test meter to the output side of the dimmer? I'm surprised the meter isn't complaining about the rough supply.
 
  • Like
Reactions: DPG
Are you testing it as an AC setting on MFT, as an A-type test, some testers do not have a variable test current to test correctly?
What tester are you using? Is any DC earth leakage present which may influence the result?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bedfordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
power fed light switch Hager rcbo won’t trip
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Alan46967A,
Last reply from
Electro-tech,
Replies
11
Views
2,372

Advert