Discuss RCBO Max Earth Loop Impedance Readings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
K
KiltedSparky
Hi all,
This is my first post on this forum, so please be easy on me.;)
We currently have new Merlin Gerin consumer units installed within Aberdeen College, and looking at table 41.3 b the eli readings should be 0.72 minus rule of thumb. This fails most of the existing circuits. When i contacted manufacturer they said to forget tables and work out readings by deviding 50 by MA present at RCBO. Can someone verify if this is correct as in regs book it gives you a table seperatly for a TT system which works with manufacturers method but not for TN system
Many thanks for advice in advance , as my next step is contacting NICEIC technical
There is general thought that if your loop imp results are under 1667 and the circuit is 30mA RCD protected then its fine on any system.
I, however would prefer to get them as low as possible regardless of the book.
Hi Kilted, welcome along.:D
As they are existing circuits that fail then yes an RCBO can be fitted as additional protection and this then technically does increase the max ZS value to 1667 ohms, overuling table 41.3 in ol' red.
The current trend that seems to be rife at the moment is that Zs no longer matters as "we can just bung it on an RCD" this I feel is not the case. In my opinion fitting an RCD to a circuit that doesn't technically need it because the Zs is too high should be a last resort and we should always do our best to get our readings within limits.
Reply to RCBO Max Earth Loop Impedance Readings in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
The heading of table 41.3 says it shows " max earth fault loop impedance Zs for Circuits Breakers..... giving compliance with 0.4s disconnnect...
So, when I did my 2391 I&t course I was told to use to values in table 41.3 of the regs for max ZS value for rcbo which provide earth fault, and...
31K
S
Anyone got any ideas? Measured R1, Rn, R2 end to end and 0.34, 0.35 and 5.6 ohm. Measured R1, R2 crossed and got between 0.21 and 0.23 ohm at...
sbelec
S
S
Hi guys had a conversation with the boss in the office after work today about a zs I got on a 32A c type rcbo bs 61009, the earthing system is...