This is my first post on this forum, so please be easy on me.
We currently have new Merlin Gerin consumer units installed within Aberdeen College, and looking at table 41.3 b the eli readings should be 0.72 minus rule of thumb. This fails most of the existing circuits. When i contacted manufacturer they said to forget tables and work out readings by deviding 50 by MA present at RCBO. Can someone verify if this is correct as in regs book it gives you a table seperatly for a TT system which works with manufacturers method but not for TN system
Many thanks for advice in advance , as my next step is contacting NICEIC technical
This is my first post on this forum, so please be easy on me.
We currently have new Merlin Gerin consumer units installed within Aberdeen College, and looking at table 41.3 b the eli readings should be 0.72 minus rule of thumb. This fails most of the existing circuits. When i contacted manufacturer they said to forget tables and work out readings by deviding 50 by MA present at RCBO. Can someone verify if this is correct as in regs book it gives you a table seperatly for a TT system which works with manufacturers method but not for TN system