Discuss rcd for fixed outside equipment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
A
alexp78
Do fixed outside devices such as floodlights (high up and out of reach) need RCD protection? Assuming cables are surface mounted (no cables buried in plaster,etc).
Are there any other conditions, such as:
- only one light per unprotected MCB, or multiples allowed?
- any other fused switch allowed to be installed after the CU?
- any labelling or marking required?
It seems that there is better overall protection afforded by actually having the lights working reliably when unattended deterring intruders, rather than catering for someone going up a ladder and forgetting to turn of the power!
Thanks.
alexp78
"Health and Safety gone Mad Cow"
Hi
If its outside it needs an RCD follow that and you wont go far wrong. If your wiring is outside it will need to be covered as the sun will takes its toll on the cable. Height of lights does not matter believe it or not the protective device fuse, mcb rcd etc is to protect the cable not the appliance.
Your lights need to have a minimum IP rating of 33 if I remember correctly. No labels required.
Any switch I would put inside if required are you intending to have the lights switch on when movement is detected and have an over ride so that you can switch them on when you want.
Chris
Thanks.
alexp78
No rcd required using stated routing of cable unless it is a TT supply
It depends on the cable size/load/mcb/voltage drop/routing etc, one light or multiples of lights is irrelevant
The lights may or may not have fused switch It may be convieniant for isolation of the lights
Labelling or marking at the consumer unit, at the relevant mcb
Wire it via a pir for security,but also via a fused spur for local isolation when required
OK, thanks.
But I've got one vote for and another against the requiement for RCD.
I'm thinking that as the protection is for the cable, then as no cables are buried, no rcd is required.
However, isn't there a requirement that there is only one circuit to qualify for no rcd? So if one 30A MCB fed several 5A fused switched spurs for local control and isolation of multiple lights...? You get the question. If it was a socket I believe you can only have one, labelled for example "freezer only".
Thanks.
Reply to rcd for fixed outside equipment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
HI folks, I'm on the management committee of the block of flats where I live. We've got ancient garage electrics and want to rewire. I have a...
Just had three split Air Con units installed at my home, the ones with an indoor and outdoor unit. I (perhaps naively) trusted the installers...
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
4K
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...