not a shelf life as such, but once installed they get dust in them, mechanisn sticks if not tested regularly, and if they keep tripping due to a fault, sometimes they get wore out. a bit like me.Thanks Dave - do RCDs have a shelf life?
not a shelf life as such, but once installed they get dust in them, mechanisn sticks if not tested regularly, and if they keep tripping due to a fault, sometimes they get wore out. a bit like me.Thanks Dave - do RCDs have a shelf life?
Eh????It's as plain as day! The CU needs rewiring correct.
Morning guys!
Over the weekend I noticed that the 80a RCD in my consumer unit kept tripping. The house doesn't have anything particularly power hungry - no air con, no DIY tools. It even trips in the middle of the night sometimes (I know so because the house alarm has a little fit when it detects there is no longer any power and switches to the backup battery).
I am wondering what it might be? I replaced the RCD with a second hand one from eBay, seller has 100% feedback and stated it was tested. Is that my issues (I replaced a duff one with a duff one) or is there something else I should look for?
Here's the unit with the switch pointed out. I have a multimeter at the ready to test, just tell me what to target.
View attachment 42840
View attachment 42841
He also doesn't know whether this second-hand RCCB purchased from eBay even works correctly...What a waste of money. It was obvious from the start it wouldn’t be a faulty RCD. You are not going to save money by doing random changes of equipment. Also it’s dangerous as you clearly are not competent to do so.....
What a waste of money. It was obvious from the start it wouldn’t be a faulty RCD. You are not going to save money by doing random changes of equipment. Also it’s dangerous as you clearly are not competent to do so.....
If called to an RCD tripping your first port of call is never to change the RCD, or randomly change any parts for that matter.Disagree about the faulty RCD .... that does happen, rarely , but ...
If called to an RCD tripping your first port of call is never to change the RCD, or randomly change any parts for that matter.
Consumer unit is a bit of a botch and a mess...but I don't see these as plain as day?? The fault would be far from intermittent and easy enough to find if it was shared neutrals.No need for any replacing of bits. First job - sort out the shared neutrals that are as plain as day!
Disagree about the faulty RCD .... that does happen, rarely , but ...
No need for any replacing of bits. First job - sort out the shared neutrals that are as plain as day!
Disagree about the faulty RCD .... that does happen, rarely , but ...
So you are saying it would be more likely a faulty RCD rather than a Circuit fault? Disagree