Thanks Dave - do RCDs have a shelf life?
not a shelf life as such, but once installed they get dust in them, mechanisn sticks if not tested regularly, and if they keep tripping due to a fault, sometimes they get wore out. a bit like me.
 
OP ............. you stated you had a spark coming on Thursday, which I presume was today - what did they find?
 
Is that really a thing? Rcds can only trip umpteen times before they get worn out?
I'd have thought they'd be designed to break their rated load 1000+ times before suffering any failure due to wear.
However I'll agree with the overall point that the op is not going to solve it quickly through trial and error!
 
The installation need testing not changing bits to see if th at bit was at fault, get an Electrician to do some investigation, and testing.
 
Morning guys!

Over the weekend I noticed that the 80a RCD in my consumer unit kept tripping. The house doesn't have anything particularly power hungry - no air con, no DIY tools. It even trips in the middle of the night sometimes (I know so because the house alarm has a little fit when it detects there is no longer any power and switches to the backup battery).

I am wondering what it might be? I replaced the RCD with a second hand one from eBay, seller has 100% feedback and stated it was tested. Is that my issues (I replaced a duff one with a duff one) or is there something else I should look for?

Here's the unit with the switch pointed out. I have a multimeter at the ready to test, just tell me what to target.

View attachment 42840

View attachment 42841


What a waste of money. It was obvious from the start it wouldn’t be a faulty RCD. You are not going to save money by doing random changes of equipment. Also it’s dangerous as you clearly are not competent to do so.....
 
What a waste of money. It was obvious from the start it wouldn’t be a faulty RCD. You are not going to save money by doing random changes of equipment. Also it’s dangerous as you clearly are not competent to do so.....
He also doesn't know whether this second-hand RCCB purchased from eBay even works correctly...
 
What a waste of money. It was obvious from the start it wouldn’t be a faulty RCD. You are not going to save money by doing random changes of equipment. Also it’s dangerous as you clearly are not competent to do so.....

Disagree about the faulty RCD .... that does happen, rarely , but ...
 
No need for any replacing of bits. First job - sort out the shared neutrals that are as plain as day!
Consumer unit is a bit of a botch and a mess...but I don't see these as plain as day?? The fault would be far from intermittent and easy enough to find if it was shared neutrals.

Look at the busbar in the original picture, the 2 MCB's to the left are also protected by the RCD in a somewhat "bespoke" arrangement.
 
Disagree about the faulty RCD .... that does happen, rarely , but ...

Not as rare as you might think I don't change that many consumer units but I have had two that had faulty RCD's brand new out the box and another that I found while doing some other work for a customer that wouldn't trip within the rated time and current about 6 months after installation
 
So you are saying it would be more likely a faulty RCD rather than a Circuit fault? Disagree

I was disagreeing with the post that ruled out a faulty RCD ....

Tripping RCD's can be caused by:

1. Issue with the incoming supply
2. Faulty RCD's
3. Earth leakage from appliances
4. N-E faults on RCD circuits
5. N-E faults on non RCD and RCD circuits
6. Faulty appliances

etc etc
 
The shower is still working but doesn't get used? The Neutral and earth are still connected even if the MCB is switched off (others have mentioned this). When RCDs trip I always think water or poor insulation resistance. I'd be tempted to remove the shower neutral & earth (and tape up) in the first instance unless it can be totally isolated? This will eliminate that circuit without an unnecessary disruption to circuits that are being used.
It does seem odd to wire the RCD in with circuits either side rather than just to the right with one length of bus bar - looks like it's been an afterthought.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Cupa

DIY
-
Joined
Location
London

Thread Information

Title
RCD in consumer unit keeps popping, replaced with new one, still same issue
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
61

Advert

Thread statistics

Created
Cupa,
Last reply from
Chivers,
Replies
61
Views
12,983

Advert

Back
Top