Hi I was doing a EICR today and went to do an RCD test will not trip when I set it to Auto come out more than 300Ms at 1 times. Did a ramp test came out 33MA what would I class this on the report any ideas would be grateful
thank neil
Hi I was doing a EICR today and went to do an RCD test will not trip when I set it to Auto come out more than 300Ms at 1 times. Did a ramp test came out 33MA what would I class this on the report any ideas would be grateful
thank neil
It's a Hager board RCD circuits are sockets up and down and shower. TNCS earthing tested at a socket there is nothing on as House is empty but MCBs where all on
Yes I operates on the RCD Test button but not through my meter I'd thought it was faulty RCD specially with it being old
I'm only doing The EICR but was unsure if what code I'd give it C3 or F1, iv thought putting 12months on cert as well
A F1 for further investigation myself I was going to put a C3 and state RCD does not operate within the trip times and place no more than 12 months till next test property is in the middle of house sale thanks
It's a Hager board RCD circuits are sockets up and down and shower. TNCS earthing tested at a socket there is nothing on as House is empty but MCBs where all on
Il put it down as C2 I am going back to test at the RCD itself with loads disconnected and see what happens, iv megger the all circuits and no issues on low readings. When I tested it at socket 1 times came up 300ms so that's why I done Ramp test. I suspected it was a faulty RCD. Thanks for your help guys
Sorry, I just assumed (obviously incorrectly) that you had carried out the test properly in the first place.
Don't code anything until you have carried out the test correctly and then think about coding it.
Why would you suspect a faulty RCD from an incorrectly carried out test? You might as well IR test a socket circuit with appliances plugged in and conclude that a cable has degraded from a low reading!!
me and geordie are old, bu tnot faulty. senile perhaps.
the recommended test interval is 10years for domestic but can be less if you feel that it is required.
The switch is held in mechanically, so in my opinion I would have tested the trip a few times before doing a final check, then act accordingly.
Then the label is a waste of time, but I do take your point.The problem with doing that is that someone isn't going to press the Test button half a dozen times before every earth fault.
Then the label is a waste of time, but I do take your point.
Then the label is a waste of time, but I do take your point.
Not really, because they should be regularly tested.
But if an RCD fails to operate when tested then it is not recommended to keep pressing the test button and retesting until it passes. The RCD has failed.
wittering. i like that word.on a par with chuntering and blathering. all words that remind me of geordies. :lipsrsealed2:If the current stream of politicians wittering about the EU,have only taught us one thing,it is some things get worse,the more you press them...:smilewinkgrin:
If the current stream of electricians wittering about the EU,have only taught us one thing,it is some things get worse,the more you press them...:smilewinkgrin:
wittering. i like that word.on a par with chuntering and blathering. all words that remind me of geordies. :lipsrsealed2:
I'd be inclined to think that there is a fault somewhere causing this if the test button works.
Dave,are you far enough down-country,to tell him"wats th urry? tamarras not touched yet,my larver..."
A particular favourite of mine,told to my mother-in-law,by a St.Ives roofer,concerning her leaking porch roof...
He returned 4 months later...and without a shred of irony,asked her to put the kettle on :shocked3:
Hahaha yes mate, I've been known to mention kettles if no offers are forthcoming after half an hour at the job.
One of the sparks I worked with during my apprenticeship once unscrewed the plug top on the kettle in front of the customer and looked at me and said the fuse seems to be good lol
Excellent ! Can you remember if the extreme hint got the required result Lee ? :biggrin:
On this principle. Would it therfore also confirm a faulty RCD if the test button didn't work and when tested, as shown in the picture, no resistance is given?
If the test button doesn't work wouldn't you change the RCD? Personally, I would so that it can be tested by the end user.
I can plug an MFT in and do a ramp test. The end user can't. Therefore I can confirm that the RCD trips within the parameters of its design, but it would need replacing to check the device regularly.