If a "cowbow" takes a very long time to relieve himself whilst out on the plains........thats a slow earth leak....
Have seen it with a few appliances where they have a earth to neutral fault usually fridges or computers but sometime on there own they aren't enough to trip RCD but some times when on together they will do or if it's one appliance it may take a while before the earth leakage trips the RCD only had this once or twice and was a ******* to fault find.
I get you now... computers, LED lamps etc have a design leakage, this is normal but what you are getting at is an accumulative leakage of several items with design leakage and/or fault leakage as this can creep past the approx 18mA which is then in the tripping territory of a 30mA rcd/rcbo.
There is a 'slow rise leakage' but this is less common and is a fault within an appliance normally where the leakage slowly ramps up until it trips rcd, this can be caused by heat expansion that creates earth leakage in proportion to temperature rise and can be seen occasionally in lighting ballasts for example, sorry to pull you on it i was more curious to what you meant as appose to having a dig.
If there is any electrician on the forum in the leicester area who would like to come and sort out problem i would be happy just to get it sorted but i dont know any myself

I know the outside lights been turned off - but just by a SP switch?
new freezer?