Have seen it with a few appliances where they have a earth to neutral fault usually fridges or computers but sometime on there own they aren't enough to trip RCD but some times when on together they will do or if it's one appliance it may take a while before the earth leakage trips the RCD only had this once or twice and was a ******* to fault find.

I get you now... computers, LED lamps etc have a design leakage, this is normal but what you are getting at is an accumulative leakage of several items with design leakage and/or fault leakage as this can creep past the approx 18mA which is then in the tripping territory of a 30mA rcd/rcbo.

There is a 'slow rise leakage' but this is less common and is a fault within an appliance normally where the leakage slowly ramps up until it trips rcd, this can be caused by heat expansion that creates earth leakage in proportion to temperature rise and can be seen occasionally in lighting ballasts for example, sorry to pull you on it i was more curious to what you meant as appose to having a dig.
 
I get you now... computers, LED lamps etc have a design leakage, this is normal but what you are getting at is an accumulative leakage of several items with design leakage and/or fault leakage as this can creep past the approx 18mA which is then in the tripping territory of a 30mA rcd/rcbo.

There is a 'slow rise leakage' but this is less common and is a fault within an appliance normally where the leakage slowly ramps up until it trips rcd, this can be caused by heat expansion that creates earth leakage in proportion to temperature rise and can be seen occasionally in lighting ballasts for example, sorry to pull you on it i was more curious to what you meant as appose to having a dig.

No worries m8 i knew what I ment I just knew it to be call it a slow earth leakage
 
My guess is a loose neutral in consumer unit(probably factory connections)....can be fine for ages and trip but not reset with load on it....fire waiting to happen as there is obviously a reason for it to trip in first place, so I would get it looked at if I were you :-)
 
If the mcbs are on and the rcd won't reset, that could be cumulative earth leakage on start up (computers, fridge etc).

The random tripping on what you have said, the socket circuits, points towards high earth leakage just below the tripping point of the rcd until an electrical item requires more current, eg fridge or something on a timer.

It also could be damp/condensation at a socket or switch with all this heavy rain we have been getting?

As said before it needs professional investigating and I wish him good luck. Please come back and tell us how it goes.
 
I know the outside lights been turned off - but just by a SP switch?

I have now isolated the outside light by disconecting wires from int connector so have to wait and see if it trips again, just a case of narrowing down possible cause one by one.
 
Think i might have narrowed it down to a 2 gang socket, the socket in question just has the washing machine plugged in to it. i tried to plug in the freezer to same socket and it trips yet when i plug freezer into its original socket it fine, yet when i plug the washing machine into it it fine as well. I have a spark coming round on Monday so at least he has a starting point.

Cannot understand why it trips when i plug in freezer but not the washing machine, if it was a fault with the freezer would that not trip it when plugged into its original socket. weird
 
It is defo the freezer causing the problem as i put both the washer and the freezer on ind RCd's and the last two trips of the main rcd the washer has been ok but freezer rcd tripped as well. So now i need to find someone to look at that,i have looked at compressor and no damp there so no idea what the problem there is.
 
Remember here Gollum your confusion has arised from the simple fact you can plug the freezer in and it may not trip, but the freezer has a control circuit and may not call the compressor for hours so can be misleading, some freezers have more complex controls too so can hide the fault until certain criteria is met e.g. some models have heating coils to maintain the freezer has differing temp as the fridge all from one compressor circuit.
 
have you considered having the freezer put onto its own dedicated circuit run seperately from the consumer unit?.
 