Were you not aware of this electromagnetic effect problem? Did they not teach you anything about this in Sparky School?I’ve added spreader box to a ryefield board using 50mm bushes however the engineer has said should be a slot as against Regs.?
Is it.? I can’t find this regulation
I’ve made the SWAs off in to the spreader box then the cables thru a series of 50mm bushes. Into the panel board521.5.1 maybe ? Not sure how you have done things though. More detail is needed after you have read that reg to see if it applies.
It isn’t a single circuit. There are 18 circuits. The circuits aren’t split as in lives and neutral they go thru as the circuits.Connecting a spreader box with a 50mm bush surely defeats the object of the spreader box doesn't it?
If you've installed the conductors of a single circuit through multiple holes in a ferrous material then this is non-compliant and you should really get an electrician to reinstall this properly.
No I’m not they go thru as circuitsAre you taking conductors through separate holes into a ferrous metal enclosure? That would be a breach of regs (Electromagnetic effects)….A slot between the holes effectively makes it one hole.
I will thank you.If all the conductors of each individual distribution circuit (including any protective conductors) go through a single 50mm bush then it is compliant. It would only be non-compliant if conductors were split. Tell the engineer he is wrong.
Is it a non Ferus Spreader box?
[automerge]1582137642[/automerge]
The spec normally come from utility supplier,they should have given you a drawing.I’ve added spreader box to a ryefield board using 50mm bushes however the engineer has said should be a slot as against Regs.?