The earthing conductor from cut out to MET is only required to be 16mm² when using the selection table and it is stated in the regulations that this is likely to provide oversized conductors, therefore using the adiabatic equation (in this case subject to the bonding requirements as well) is a better and more comprehensive design.
There is no decrease applicable from MET to CU because of the size of the switch fuse as it is the same size (probably) as the cut out fuse and in both cases would be overidden by the bonding requirements.
There is no decrease applicable from MET to CU because of the size of the switch fuse as it is the same size (probably) as the cut out fuse and in both cases would be overidden by the bonding requirements.