Duetto96
Hi Folks,
I have a working, but redundant, shaver socket mounted on a bathroom studwall that I need to remove. That shaver socket is wired into the lighting ring and when removed, each side of the ring will need to be joined back together. That joint/connection will be inside the stud wall about half way up the wall and will not be accessible after it has been tiled over. What is the official way to make this connection? Should I use a regular junction box a connector block or do the wires need crimping, soldering or what?
I'm assuming that even though the shaver socket is currently in the bathroom, it wont be after its removal and therefore this is not a notifiable alteration. Is this correct?
Thanks,
David
It's unlikely that you have a lighting ring, most likely a radial.
It's also unlikely that you will have to cables to the shaver socket, unless it then feeds something else, such as a fan, or a light over a mirror.
At present, the cables should be in a prescribed zone, either vertically or horizontally in line with the shaver socket.
If you remove the socket, and not the cables, the cables may no longer be in a prescribed zone.
Such is not allowed by either the wiring, or building Regulations.
Thanks. Some extra info... Definetely two cables one from above and one from below. They run vertical in line with the socket. The socket goes dead when I switch the upstairs lighting ring off at the consumer unit.
if you are trying to keep the cost down and dont want to get a sparks in, can you not incorporate the shaver socket back into the bathroom design even if you dont use it, then your job would still comply....
Where does that go if as you say you isolate the upstairs lighting and it goes off. Is that the main feed from the CU?
That would be my reading on it - the vertical from below is the start of the feed. If it's inside the stud though, it could be clipped at 50mm (or more if deeper) where it's accessible and then wouldn't really be a major concern as far as zones - not ideal, but have seen a whole lot worse crimes!
Crimp and shrink, or use an MF juntion box like the Ashley ones.
Thanks for the help. The original shaver point is (was) in a location where a shower is soon to be. Given the location, all I want to do is make the joint secure and forget about it. Not sure I would want or need to incorporate that joint into the bathroom design.
The shaver socket is now removed and the two sides of the cable are temporarily reconnected using a connection block. All I was looking for was some advice on the proper way to permanently connect the wires back together given that they will be inaccessible once the plasterboard is tiled over. I like the idea of the ashley MF box so I think I'll run with that if I can find one.
That will still not get you past the fact that you have a buried cable, that will now not be in a prescribed zone.
OK I hope it will be RCD protected, but it still will not conform to the regs unless you give it earthed or mechanical protection.
If your doing all this work, could you not rewire the cable? Could you remove the large box and fit a smaller one and put a waterproof cover on it?
Removing a bathroom shaver socket
Australia
Duetto96,
MarkieSparkie,