Going through a ring main design calc for a course I’m on to determine c.s.a of ring final conductors.
As we don’t know the load current for circuit we assume this to be the rating of the overcurrent protection device. I.e 32a.
Only correction factor I need is grouping factor which is 0.45.
32 / 0.45 = 71a
Meaning I should use 6mm ring? Speaking from experience this is never the case. Am I missing something?
 
first, as it's a RFC, you assume a max. current of 26A in each leg as a worst case. and can't see 0.45 being the correct factor.
 
The circuit is grouped with 12 other circuits giving 0.45 grouping factor. it = in / cg

- - - Updated - - -

it = 32 / 0.45 = 71a
 
not enough info. for example, if any cables are loaded no more than 30% of their rating ( grouping allowed for), they can be ignored when calculating the grouping factor for your circuit/s.
 
Basic maths, let's assume your derating factor is 0.5 for easy reckoning, if you divide 32 by a half, you are effectively doubling it! If, however, you multiply 32 by half, you'll get 16......which may well fit in more with your line of thought. However, it's an outrageous derating factor! :)
 
Telectrix I did read that somewhere. The circuit in question is grouped with 12 other circuits. All which are socket circuits apart from 2. As we cannot fully determine the design current for these circuits and how they will be loaded, can we just use grouping factor for the two circuits. it 32 / 0.7 = 45a, which seems more reasonable.
 
The way I would think of it is whatever current capacity you require after applying factors etc .... this is for a radial circuit. Assume in your case a 6mm cable is required (i.e. 1 cable going into the socket). For a ring circuit you have two cables going into the socket so each needs to be 3mm to give you the effective 6mm. Cant get 3mm so would do a ring in 4mm --- whether you'd get them into the back of the socket though is another question!!
 
buy decent sockets and it's easy to get 2 x 4mm into them.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Ring main design calc
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
SafetyEICR,
Last reply from
telectrix,
Replies
10
Views
5,131

Advert

Back
Top