Hi all, daft thing to be doing at this time on a Saturday night I know but is there a reg that specifically says we must bring the installation or part of it up to the current standards if we alter it?

Also is there specifically a regulation stating that earth bonding must be upgraded or installed when changing a consumer unit
or is this just implied/best practice?
 
The regulations are not retrospective and installations do not have to be brought up to current standards. This is in the introduction.

132.16 requires that the installation be adequate and safe for any alteration or addition including earthing and bonding. This does not mean they need to be brought up to the current standard.

The regulations in general apply to all new work, but not all parts of existing installations.
 
The regulations are not retrospective and installations do not have to be brought up to current standards. This is in the introduction.

132.16 requires that the installation be adequate and safe for any alteration or addition including earthing and bonding. This does not mean they need to be brought up to the current standard.

The regulations in general apply to all new work, but not all parts of existing installations.
This is exactly the reg I’m after :rolleyes: I think I haven’t been clear as to what I meant by bringing the installation up to current standards... what I was meaning was for example sticking in an RCBO in place of an MCB when you add in extra sockets etc
 
This is exactly the reg I’m after :rolleyes: I think I haven’t been clear as to what I meant by bringing the installation up to current standards... what I was meaning was for example sticking in an RCBO in place of an MCB when you add in extra sockets etc

Ok, so in that specific example we can start with 132.16, verifying the earthing and bonding are adequate before we start work. All equipment to be used, CU and associated existing wiring and containment if any, are suitable for continued use.

RCD additional protection should be provided for sockets that you add, but not all existing sockets on that circuit need comply. Sometimes RCD protection at the circuit origin can be easiest though. All new work would need to comply with all general rules in BS7671
 
RCD additional protection should be provided for sockets that you add, but not all existing sockets on that circuit need comply.
As in most cases would the cable feeding the new sockets and the method of protection ie RCD spur etc so most of the time sticking in an RCBO would be the best way forward
All new work would need to comply with all general rules in BS7671
And so when replacing a consumer unit having altered the characteristics of each circuit care must be taken to ensure that there are no latent faults or dangerous situations which may be present in the installation.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

MFS Electrical

Mentor
Arms
-
Joined
Location
Scotland, Inverclyde, Greenock
Website
http://mfselectrical.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
SJIB/SECTT recognised apprenticeship.
SVQ level III electrical installation.
City and guilds 2382 (18th)
City and guilds 2391-52 (I&T)
City and Guilds 2919 (EV Charging)
Business Name
MFS Electrical

Thread Information

Title
Searching for regs
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
MFS Electrical,
Last reply from
Wilko,
Replies
5
Views
1,202

Advert

Back
Top