spud1

-
Arms
Hi,

So I was reading the notes on regulation 531.3.5.3.2.201 (Page 156) today and noticed Note 1 that consideration should be given (Where TT earthing is present) to the manufacturer's internal line cable links on the supply side of an RCD being insulated AND sheathed! Does anyone know of any distribution equipment manufacturer that either fits double insulated cable links as standard or offers an alternative double insulated kit of leads?

Cheers
 
Best to use an S type 100ma RCD main switch with a tails gland making sure it enters as close as possible to the incomer. Internal links are then covered. If you are using RCBO's they must be DP or switched N if you have an RCD main switch.
 
has anybody ever seen internal links damaged and shorting out to a metal case CU? I certainly haven't.
 
No I’ve not seen any insulated and sheathed internal cabling. Nor have I seen internal links flailing about, but it is a possibility I guess.
 
Taken from Hager’s CU instructions

TNC-S, TN-S when installed in an electrical installation complying with BS 7671
Hager recommends for TT systems a 100A type S time delayed RCCB or a main switch with RCBO protection only on all outgoing circuits.
 
Last edited:
Taken from Hager’s CU instructions

TNC-S, TN-S when installed in an electrical installation complying with BS 7671
Hager recommends for TT systems a 100A type S time delayed RCCB or a main switch with RCBO protection only on all outgoing circuits.
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
 
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
No it’s a main switch with rcbo’s or dual rccb’s with an S type upfront is what they mean, ( I think).
Not very clear but that would make more sense.
30FDBE3B-FEAF-4DEF-A239-6340054ED0FA.png
 
Hi,

So I was reading the notes on regulation 531.3.5.3.2.201 (Page 156) today and noticed Note 1 that consideration should be given (Where TT earthing is present) to the manufacturer's internal line cable links on the supply side of an RCD being insulated AND sheathed! Does anyone know of any distribution equipment manufacturer that either fits double insulated cable links as standard or offers an alternative double insulated kit of leads?

Cheers
They aren't double insulated they are insulated and Mech protected, never seen a cable with the double insulation marked on it.
 
They are wrong if they are recommending an RCD main switch with SP RCBO's. A fault on a final circuit will not disconnect the neutral and probably take out the main switch as well
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
 
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
I think radiohead's point is if a final circuit has a N-E fault then you will probably trip the incomer RCD as the SP RCBO will trip but not isolate the neutral fault.

So it is not necessary according to the regs as such, but it is far better to have a N-switching RCBO if you can. I guess it indirectly comes under the requirement for selectivity, etc (off hand don't remember the numbers).

Not that many do unfortunately, but at my last count Wylex/Crabreee/Fusebox (the miniature version) RCBO for consumer DB do switch neutral.
 
There is no requirement for a protective device to isolate the neutral under fault conditions, regardless of earthing system type.
You miss the point. The requirement is that a single fault on a final circuit does not disconnect the entire installation. If there is an RCD main switch failure to disconnect the N on a faulty final circuit will probably disconnect the entire installation. Because of an indirect consequence of a single fault it is in effect a requirement that where an RCD main switch is used with RCBO's then each RCBO must disconnect both poles.
edit...post crossed with PC1966
 
Back to the OP's point - I really think that any properly installed metal CU is going to be fine.

I.e. where the tails are double-sheathed as expected, they enter by a proper gland for support and protection from damage, and the CU has been installed with care to make sure the busbar is in place and clamped correctly, etc.

Obviously all circuits have to be RCD protected as TT rarely will have a Zs able to disconnect a MCB, and at that point I would state my personal preference for both an up-front 100mA/300mA delay RCD and then whatever 30mA instant RCD/RCBO are needed for "additional protection".

In my case it is less about the risk of an internal CU short, than about the risk of a 30mA RCD failing to trip and so the earth/CPC remains live for a prolonged period. With an incomer RCD there is no single point of failure.
 
Last edited:
You miss the point. The requirement is that a single fault on a final circuit does not disconnect the entire installation. If there is an RCD main switch failure to disconnect the N on a faulty final circuit will probably disconnect the entire installation. Because of an indirect consequence of a single fault it is in effect a requirement that where an RCD main switch is used with RCBO's then each RCBO must disconnect both poles.
edit...post crossed with PC1966

When were Wylex/Crabtree SP&SN RCBO's first introduce? I have a feeling that many TT installs have been none compliant since July 2015, if that's the case.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Should internal links in consumer units be double insulated where TT earthing is present
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
spud1,
Last reply from
Midwest,
Replies
17
Views
3,742

Advert

Back
Top