Looks good mate, as I have never heard of it, whats it for? haha!
Not sure either but I'd hazard a guess at lightning protection maybe. Damn neat install though
Discuss **Show Us Your Installs!!!** in the Australia area at ElectriciansForums.net
Looks good mate, as I have never heard of it, whats it for? haha!
Not sure either but I'd hazard a guess at lightning protection maybe. Damn neat install though
Well that's a different story, I thought it was a domestic/small commercial premises but it makes sense in a sub station.It's a Scottish power secondary substation 33kV I believe but not sure as the LV install and ally tape were as far as I got before they snapped the padlock on.
It's a Scottish power secondary substation 33kV I believe but not sure as the LV install and ally tape were as far as I got before they snapped the padlock on.
I believe that Scottish Power are now moving to aluminium for all there cabling also due to the high price of copper, was on a H.V course at there training centre a few months back and thats what the instructor was saying.
Yep, this is a standard requirement for sub-station rooms/buildings. Never, ever seen this done in aluminium though. That is possibly going to create more problems than it's initial cost reduction!!
Normally the two ends of this room loop would connect to a MET/MET earth bar, with removable links to facilitate testing. One section of the earth bar would connect all the earthing conductors, such as earth rods, Ufer earth mat, etc, and a second section would contain electrical links from cables TX, switch boards etc. The tape would be used to locally connect and equalise other metal structures or componants within the room, like the metal doors, windows (if any) ventilation louvers and other metallic plant, like AC units and/or it's ducting etc....
We're hoping to have a few more of these of the back of this then doing them quite regular if everything goes ok. Will be interesting to see if the other ones we do are aluminium or copper tapes.
Look at the DNO’s current specifications for substations. Aluminium is permitted for earthing.
Not saying I like it, but it’s permitted.