EICR observation - Electric shower does not have an isolator (pull cord or switch). Circuit can be isolated and locked off in the consumer unit which is in the nearby airing cupboard. (This is 1st floor flat).

Is there a reg that says a shower should have a local isolator?
 
Not sure what you guys want me to add. I've said what I will probably do in post #10. Didn't quite manage to complete all tests yesterday so have to return one day next week, which gives me time to ponder some more!

Will probably include it in the observations but without a code. That way I've mentioned it but it won't affect the satisfactory/unstaisfactory conclusion.

Could extent this discussion further by the fact that the installation only has RCD protection on 1 circuit - on the shower which appears to have been added after the refurb was completed about 20 years ago. Flat is on the first floor. Discuss!
Yellow, you are the guy on the job, if you feel to put a code 3 in, that is absolutely fine, it is only a recommendation, still satisfactory on the report. That would be my take only because that is my opinion, because I like local isolation.It will be up to the client at the end of the day.
 
Not sure what you guys want me to add. I've said what I will probably do in post #10. Didn't quite manage to complete all tests yesterday so have to return one day next week, which gives me time to ponder some more!

Will probably include it in the observations but without a code. That way I've mentioned it but it won't affect the satisfactory/unstaisfactory conclusion.

Could extent this discussion further by the fact that the installation only has RCD protection on 1 circuit - on the shower which appears to have been added after the refurb was completed about 20 years ago. Flat is on the first floor. Discuss!
Why do we need to discuss it? Your doing the EICR? You challenged me that I was doubting your professional ability.
 
Why do we need to discuss it? Your doing the EICR? You challenged me that I was doubting your professional ability.

I just thought I'd let you guys mull that over! I'm sure there will be different opionions out there!

Ok, I'll start with my take. Plenty of C3's, lack of RCD protection on bathroom circuits (light + heater), no RCD protection for concealed cables, no RCD protection on sockets. The only possible C2 could be lack of supplementary bonding between shower/heater/lights in bathroom, but since the consumer unit is in the adjacent airing cupboard I suspect resistance between circuit earths will be OK, but will check!
 
You mean, you want the forum in general to instruct you as to how to do your job? You are undertaking an EICR, it's a tricky old number requiring quite a lot of things, experience, qualifications and so on. Have you got any?
 
You mean, you want the forum in general to instruct you as to how to do your job? You are undertaking an EICR, it's a tricky old number requiring quite a lot of things, experience, qualifications and so on. Have you got any?
I don't want the forum to instruct me in anything I've just told you want I'm going to do, but I know others will disagree and thats their perogative.

As for experience and qualifications I probably have more than you!

I'm now leaving this thread with no further input!
 
I don't want the forum to instruct me in anything I've just told you want I'm going to do, but I know others will disagree and thats their perogative.

As for experience and qualifications I probably have more than you!

I'm now leaving this thread with no further input!
Oh dear well that's an awful shame. It just seemed to me that every time you get a bit of a problem you come on here and ask how others would tackle it, not the sort of form for one which such an impressive pedigree? Maybe it's just me....
 
Oh dear well that's an awful shame. It just seemed to me that every time you get a bit of a problem you come on here and ask how others would tackle it, not the sort of form for one which such an impressive pedigree? Maybe it's just me....
I don't think there is any need Sparks to rip into the guy, we all here to share our experiences and OPINIONS. Listen to uncle Dave.
 
as for me, i've had enough of bloody showers. rain all week, getting soaked just getting gear off van, bugger it. time for beer.
 
snow showers in cheshire atm. pink floyd on the stereo, old peciliuer in the glass, dogs swarming over me. me happy .
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dorset

Thread Information

Title
Shower isolator
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
59
Unsolved
--

Advert

Thread statistics

Created
yellowvanman,
Last reply from
Hellmooth,
Replies
59
Views
18,743

Advert

Back
Top