OP
baldsparkies
Wotsit,
I am going to make a very bold statement, 8 meter run of 6mm t/e clipped direct 40A BS EN 60898 typeB protective device complies with all current regs and no problems with a 9kw load or volt drop
So what exactly are you trying to prove here ?? after all the resitivity of a conductor is proportional to its cross sectional area, and inversely proportional to its length provided the temperature remains ambient. But then you already know that
I am going to make a very bold statement, 8 meter run of 6mm t/e clipped direct 40A BS EN 60898 typeB protective device complies with all current regs and no problems with a 9kw load or volt drop
So what exactly are you trying to prove here ?? after all the resitivity of a conductor is proportional to its cross sectional area, and inversely proportional to its length provided the temperature remains ambient. But then you already know that