Can you confirm that all the outgoing neutrals have been disconnected from the neutral bar on the RCD that trips...
 
Switching off the MCB will not affect the fault as it is on the neutral that is not switched off.
You need to find the fault on the lighting circuit and testing of the circuit will do that for you, to some extent.

Little diagram to clarify (or mess up) your approach
NE fault RCD trip on current use.jpg

EDIT: Just too late fault is found, typical!!:sick:
 