Customer moved into a 4 bed property a couple of months ago and has just had an electricity bill for £500 for one month !
I was called out to find out what was causing such a large bill, and found out that the immersion heater had been left switched on permanently.
During my inspection of the electrical installation I discovered this main isolator.

Apart from the obvious 2.5 cable fused off a 100A fuse to feed a sw spur for the local light, my main concern is the 2 SWA cables that have been used as a sub main to feed the house.
The incoming supply is only single phase but is connected to a 100A service connector and 3 lots of meter tails feed into this switch fuse. The outgoing 3 core SWA cable is then used as a sub main to feed the phase conductor to a 3 phase distribution board in the house.
A further 2 core SWA has been used to take the neutral and earth conductors to the same distribution board.
This obviously does not comply with the regulations as these would in effect be classed as single conductors, & eddy currents could be present in both SWA cables !
Do you think that this could also contribute to the high electricity bills ?
I was called out to find out what was causing such a large bill, and found out that the immersion heater had been left switched on permanently.
During my inspection of the electrical installation I discovered this main isolator.

Apart from the obvious 2.5 cable fused off a 100A fuse to feed a sw spur for the local light, my main concern is the 2 SWA cables that have been used as a sub main to feed the house.
The incoming supply is only single phase but is connected to a 100A service connector and 3 lots of meter tails feed into this switch fuse. The outgoing 3 core SWA cable is then used as a sub main to feed the phase conductor to a 3 phase distribution board in the house.
A further 2 core SWA has been used to take the neutral and earth conductors to the same distribution board.
This obviously does not comply with the regulations as these would in effect be classed as single conductors, & eddy currents could be present in both SWA cables !
Do you think that this could also contribute to the high electricity bills ?