Hello all. I have visited a domestic property with two consumer units, one downstairs and then a separate one for upstairs. The upstairs is fed by a 16mm twin and earth and the downstairs is fed by 25mm tails. The cu downstairs is a duel RCD. The question I want to ask is, since the cable feeding upstairs is buried, I was planning to install the sub main directly into downstairs consumer unit. However. The problem is the issue with conflicting RCD. I don't want nuisance tripping occuring since the RCD downstairs is only rated 30ma. I was under the impression that time delay rcbo were easily available but after a bit of shopping around, it's not the case. This was my initial idea on how to resolve the issue. Thank you in advance
 
A time delay RCD is not suitable for the additional protection required for cables buried in walls at < 50mm.
Possible options might be:
1. Add a small consumer unit for the sub main with it's own RCBO, by tapping into the tails before the main consumer unit.
2. I can't think of anything else.
 
With the 16mm T&E buried you simply cannot avoid the requirement for RCD protection at the feed end

You can change the T&E to SWA if its an easy run but apart from that you are stuck with the front loaded RCD
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham
Business Name
Electrical solutions

Thread Information

Title
Sub main in a domestic property
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Zahid Nawab,
Last reply from
freddo,
Replies
3
Views
4,590

Advert

Back
Top