Hi guys I have just done an Eicr and 1of my findings was that the fire alarm panel was fed by SWA and I am wondering if that needs replaced with fp200 or similar?
Thanks in advance
Kenny
Thanks in advance
Kenny
Do you mean from a LSZH point of view or a high temp survival point of view?You need to specify the type of swa as it may be compliant.
BS7671 makes reference to supplies for safety systems hence it is relevant.the fact that the fire alarm is fed in SWA is irrelevant to your EICR as long as the SWA complies with BS7671. i.e it'ssuitable for the load; it is installed in accordance with BS7671 (glanded properly etc.). Your EICR has no relationship to BS5839.
Pretty sure it's just standard SWA but I would need to double checkYou need to specify the type of swa as it may be compliant.
i worded that badly. what i meant was that your EICR does not relate to whether or not it complies with BS5839, as long as it complies with BS7671. although a comment could be made to make customer aware.BS7671 makes reference to supplies for safety systems hence it is relevant.