Be honest here guys...When you do your testing, do you do it exactly the same as you would during a college assessment on every installation you work on/install
I dont, and I've never known a sparky who does
Feel free to accuse me of being a cowboy but here are the things I do different...
If im IR testing an old install and I get, say 50Mohms across the main Neutral/Phase and earth bars I'll write down every circuit as >200 rather than rip the fuseboard apart trying to find the circuit/circuits with less than 200. It doesn't really acheive anything IMO and takes time..
I never IR 500volts between L and N on an existing installation if the reading to earth is good, the risk of damaging the clients property is too great IMO
If im testing a new ring circuit installed by myself I'll test end to end on all 3 conductors but won't carry out cross connected ring continuity tests. On my own circuit I know its wired as a ring so this test is completely pointless.
On my own installations, if I know the chances of parallel paths etc are zero I sometimes gain my R1+R2 reading for a radial by testing Zs at the furthest point and deducting Ze. IMO this proves beyond all doubt you have a good R2. Now I know you're supposed to prove the circuits are compliant before energizing but we're all trying to make a living here and whats the worst that can happen when you know you do good connections every time and its all RCD'd
Also when I do a consumer unit change I do not test and inspect the installation to the same extent as I would an EICR. I just test ring end to end, IR L/N-E, RCD time, Ze and Zs at the end of each circuit-The going rate for C/U's (£350) does not really allow for a whole day of testing and inspection and the house is gonna be 10 times safer than before I turned up anyway.
Hopefully this should arouse some fiery debate
Seems a bit of a case of common sense vs blindly following the rules you've been given without questioning the neccessity....
I dont, and I've never known a sparky who does
Feel free to accuse me of being a cowboy but here are the things I do different...
If im IR testing an old install and I get, say 50Mohms across the main Neutral/Phase and earth bars I'll write down every circuit as >200 rather than rip the fuseboard apart trying to find the circuit/circuits with less than 200. It doesn't really acheive anything IMO and takes time..
I never IR 500volts between L and N on an existing installation if the reading to earth is good, the risk of damaging the clients property is too great IMO
If im testing a new ring circuit installed by myself I'll test end to end on all 3 conductors but won't carry out cross connected ring continuity tests. On my own circuit I know its wired as a ring so this test is completely pointless.
On my own installations, if I know the chances of parallel paths etc are zero I sometimes gain my R1+R2 reading for a radial by testing Zs at the furthest point and deducting Ze. IMO this proves beyond all doubt you have a good R2. Now I know you're supposed to prove the circuits are compliant before energizing but we're all trying to make a living here and whats the worst that can happen when you know you do good connections every time and its all RCD'd
Also when I do a consumer unit change I do not test and inspect the installation to the same extent as I would an EICR. I just test ring end to end, IR L/N-E, RCD time, Ze and Zs at the end of each circuit-The going rate for C/U's (£350) does not really allow for a whole day of testing and inspection and the house is gonna be 10 times safer than before I turned up anyway.
Hopefully this should arouse some fiery debate
Seems a bit of a case of common sense vs blindly following the rules you've been given without questioning the neccessity....