Discuss time delay RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi guys, Got a TT system. Do I need to install a time delay RCD on an old Wylex board that is supplying off-peak night storage heaters. The unrestricted board has been changed to 17th last year but the restricted board has not been changed.
Cheers. The external Ze is very good at 0.18.
I think e54 installed that earth pit. If it is tt, it should have one too cover both boards, don't need two. On the incoming tails before wiggles off in all directions..
even by flying eng54 all the way from china to install a TT earthing system, i'd be amazed at that Ze. must have a rod down to Oz to get 0.18.
The TT system, if that's what you've got, doesn't require a RCD as long as the disconnection times can be met, 41.1, then 411.5.2 can be considered as sufficient.
As for E54 flying over to inspect a pit, he'll probably condemn it for using a twigg - lol
That's why I'm going out to check it later this week. One of our other sparks did an EICR on it last week, gave me the cert to sign off, as QS, and I refused. He wondered why! Also noticed other discrepancies like 2.5 lives and 2.5 cpc with him specifying PVC/PVC type used. Challenged, it now appears type C.
I just thought as might not be stable , just use rcd even 30mA on the board without. But I ain't a electrical legend yet , just a chancer.
I am with you 100 % . It may be a first class Ra at the moment but no matter how deep you go , unforeseen external circumstances may change this far before its next inspection ( Unlikely , but not impossible ) ! I am not advocating the reliance of an rcd , but for TT systems it just makes sense to have as a added security !
there's no way he's got a Ze of 0.18 on a TT system. someone's telling porkies.either that or his pi$$ is marketable.
I can't understand why people do not believe what's written in BS7671. If its a TT system with a Ze of 0.18 Ohms after the MPB have been disconnected then 411.5.2 (ii) is sufficient. We used to work to that all the time 20 odd years ago.
However, I've never seen a TT system as low as that. Maybe 0.5 - 1.5 Ohms.
It is possible , I have personally seen it on an ex military site that we look after and is now a farm . I can not remember the exact Ra now as it was a few years ago , but I have posted about it before ( I can only go back as far as the date of my user name change , for some reason ) in a post about a 100 Ma time delayed RCD going out before the 30Ma RCD down stream , and it was because of the exceptionally low Ra at source .
Maybe so , but for the price of them I would rather err on the side of caution and have it as a secondary safety net anyway . No matter what others will no doubt preach , I have seen more than enough Ra's rise and fall , ( Not just the twigs ) far more than I would like to see .
I agree with all here, that an Ra of 0.18 ohm on a typical domestic TT system is going to be extremely hard to believe!! lol!! You'd have to be driving a deep rod into a salt marsh to stand any chance of seeing that sort of value!!
As for the Very low Ra on an ex military site, that i can believe, there are probably multiple linked deep driven rod positions around the site, or a full dedicated earth field in place...
On the majority of standard domestic, small/medium commercial systems it is Always prudent to provide the extra back-up protection of an up-front 100/300mA S type RCD device. No-way would i rely on a single RCD device as my sole means of earth fault protection. They are just not that reliable!!
Reply to time delay RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...