Discuss volt drop query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
zone77
When doing a volt drop calc for a sub board, is the max volt drop 5%(11.5v) ( the sub board feeds lighting and power circuits) or is it reduced to 3% (6.9v):confused:
Does it not matter if its for public or commercial use, or am I confused?.
Just looked in BRB and it says
Public lighting 3% other 5%
Private 6% other 8%
Ah and just reading your post agian I see your point I would go with 5%.
If the sub-main is feeding lighting circuits, the the max VD from the origin to the end of the lighting circuit fed from the sub-main DB is 3%.
VD is calculated from the origin of an installation in this case the house so you must include the sub-main as part of the lighting circuit.
This is from the ECA.....
Answer by the ECA: The overall voltage drop limit is 3% (6.9V) single-phase, if the sub-main is feeding lighting circuits.
Zone 77 it dosnt matter where it is. f its from the public supply thw max volt drop from Origin is
lighting 3%
power 5%
When its designed you will find distribution cables may be oversizes so less volt drop so it can be allowed for on the final circuits.
Reply to volt drop query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...