Pricing up a job in a factory and have to wire in a 3 phase supply, just going to double check my cable sizing i calculate i need to use a 10m cable

Swa cable clipped direct on its own , 35m run feeding a unit needing a 3 phase 20amp supply am i right ? just seems a little on the heavy side ?
 
top of my head 2.5mm is on the limit of VD. 4mm or 6mm is adequate.
 
Thanks David , coming in at a more sensible size now knew that looked far to heavy

- - - Updated - - -

4mm is the baby was some how working on the wrong volt drop allowence
 
Cable type: 70 deg.C Multi (armoured)
Fixing method: Clipped direct

Protection device: CB typeC
Protection rating: 20 A

Cable size: 2.5 mm
CPC size: 2.5 mm
Current carrying capacity of cable in this instance: 25 A

Final circuit: Yes
Ambient temperature: 30 deg.C
Number of cables grouped: 1
The cables are spaced


Voltdrop: 2.62 %
Allowable voltdrop: 5.00 %

Length: 35.0 m
Calculated R1+R2: 0.519 ohms
Calculated Zs: 0.87 ohms
Maximum Permitted Zs: 0.92 ohms

Type of system: TN
Supply: Three phase at 400 v
Ze: 0.350 ohms
Fault current: 0.26 kA

Applied correction factors:
Ca: 1
Cg: 1
Ci: 1
Cc: 1


Using a app I have it says 2.5mm2 is fine, although I would personally use 4mm2
 
with 2.5mm i get vd of (18 x 20 x 35)1000 = 12.6V , just over 5% then you have to allow a bit for the outgoing cable/s on the load side.

sorry, wrong column. 15mV not 18. so VD = 10.5V so acceptable.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Gloucestershire

Thread Information

Title
Volt Drop
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
huntos33,
Last reply from
telectrix,
Replies
7
Views
1,584

Advert

Back
Top