Pedantic I know...!
BS1362 fuse.
Zs @ 0.4s, 3A = 16.4, 13A = 2.42 ohms.
BS1362 fuse.
Zs @ 0.4s, 3A = 16.4, 13A = 2.42 ohms.
Discuss Voltage drop and ZS - Some thoughts in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Pedantic I know...!
BS1362 fuse.
Zs @ 0.4s, 3A = 16.4, 13A = 2.42 ohms.
Where are those figures from Archy?
if you look on the page beofre mate, they are there at the bottom.Found them here...
http://www.shepleyelectricalservices.com/Max%20ZS%20Table.pdf
BRB only gives 5sec Z esses for 1362s.
Look upon the supply to the FCU as a distribution circuit with protection from a B32A MCB and the final circuit from the FCU with protection from a BS1362 fuse.
You could add a second schedule of test results just for the final circuit from the FCU, treating the FCU as a distribution point.
Volt drop is measured from the origin of the installation.
Yes understood but a minor works would also meet the regs because it is not "a new circuit"
So using an FCU it can be an extension to an existing circuit, as well as a new circuit added to an existing distribution circuit.
How does a FCU differ to a 1 way CU? Both have DP isolation, both have an OPD and max Zs values of BS1362 fuses are printed in BS7671 so why can't we add a separate schedule of test results for the outgoing side of a FCU?
DB reference - FCU/1
Location - Kitchen
Zs at DB - 0.38ohms
Ipf - 0.61kA
blah blah blah!
If the maximum Zs of the load side of the FCU is less than that allowed by a B32 MCB then you may not need to go to that length but if it ends up being higher due to the length of the circuit then by treating the load side individually you can show that the max measured (or calculated) Zs is within limits for the chosen BS1362 fuse.
Just thinking out of the box
Malcolm, it was more tongue in cheek about comparing a FCU to a consumer unit but reading the definition of a distribution board a FCU does seem to have similar, if not the same attributes.
My main point was a separate schedule of test results could be documented for the load side of the FCU, nothing at all wrong with that, especially if the measured Zs at the end of the circuit falls outside the limits of the protective device for the supply side of the FCU. In the OP's case the supply to the FCU is from an existing ring final with a disconnection time of 0.4s. I would also document a disconnection time of 0.4s if the supply to the FCU was also a radial.
So lads where are we going to place the cheesecloth when we carry out the 16Ka test on this spur unit as is required for all distribution boards to BS EN 60439 UK Annex ZA
Gary I know your post was tongue in cheek but i'm afraid you have now got people agreeing with you that a BS 1363 accessory is going to afford you the same standards as a Distribution Board in a domestic situation as per BS EN 60439 UK Annex ZA.
As I said mate it is a dangerous road