Look upon the supply to the FCU as a distribution circuit with protection from a B32A MCB and the final circuit from the FCU with protection from a BS1362 fuse.
You could add a second schedule of test results just for the final circuit from the FCU, treating the FCU as a distribution point.

Volt drop is measured from the origin of the installation.
 
Look upon the supply to the FCU as a distribution circuit with protection from a B32A MCB and the final circuit from the FCU with protection from a BS1362 fuse.
You could add a second schedule of test results just for the final circuit from the FCU, treating the FCU as a distribution point.

Volt drop is measured from the origin of the installation.

Yes understood but a minor works would also meet the regs because it is not "a new circuit" in itself. Horses for courses I suppose! :smile:
 

Reply to Voltage drop and ZS - Some thoughts in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock