I'm pretty sure a BS1362 fuse is rated to break 6kA, more than likely same as the B32 MCB supplying the FCU.
You'd need a Zs of 0.038ohms at the incoming side of the FCU to see fault currents that high anyway which is pretty unlikely!
Where a 60439-3 (and 5486-12) CU comes into it's own is with a type 2 1361:1971 fuse rated at no more than 100A - with this combination the short-circuit rating of the protective device in the consumer unit may be taken to be 16kA. However, it's extremely unlikely to see anything near that value unless you like at the side of a substation.
You'd need a Zs of 0.038ohms at the incoming side of the FCU to see fault currents that high anyway which is pretty unlikely!
Where a 60439-3 (and 5486-12) CU comes into it's own is with a type 2 1361:1971 fuse rated at no more than 100A - with this combination the short-circuit rating of the protective device in the consumer unit may be taken to be 16kA. However, it's extremely unlikely to see anything near that value unless you like at the side of a substation.