I'm pretty sure a BS1362 fuse is rated to break 6kA, more than likely same as the B32 MCB supplying the FCU.
You'd need a Zs of 0.038ohms at the incoming side of the FCU to see fault currents that high anyway which is pretty unlikely!

Where a 60439-3 (and 5486-12) CU comes into it's own is with a type 2 1361:1971 fuse rated at no more than 100A - with this combination the short-circuit rating of the protective device in the consumer unit may be taken to be 16kA. However, it's extremely unlikely to see anything near that value unless you like at the side of a substation.
 
It is extremely unlikely that you really need 25/16mm tails, in a domestic situation how many of us have seen a nice set of 4/6mm tails or I should say 7/036 or 7/044 jogging along nicely for 40 odd years without any sign of burning.

And I'm sure that even if you doubled a Zs value on a protection device it will be extremely unlikely not to trip within it's parameters.

And it is extremely unlikely that someone will get fatally electrocuted in their home........................
 

Reply to Voltage drop and ZS - Some thoughts in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock