P
Paul Langham
One switch return is in JB, but there is only room for one in the JB im led to believe ???Need at least five terminals, neutral, line loop, earth and two switch returns.
Thanks Archy for your help, so what cables would you actually terminate into the 3 way terminal block ?
Ok no worries i will get it on here for you guys, many thanks for your helpI think we'd all like to see a picture of that and a copy of the actual question.
Top job Paul.Hi mate, i have done this, many thanks for your help
Yes it is a 6 way JB, so can you have 2 switch lives going into the JB, because i dont see there being any room ?You need a 6 way junction box...
It is a 6 way JB murdochYou need a 6 way junction box...
hi mate, it is two seperate lights from 1 circuit but both lights need a seperate switch ?
ok thanks, but would you be able to terminate 2 switch lives into the JB, would there be room ?That makes a lot more sense, this is perfectly possible and acceptable from one 6 terminal JB.
Yes there is two switch return terminals in the JB, but can these be used for two different switches ?When you say room do you mean space or enough terminals. You need the loop line, neutral, cpc and two switch return terminals, five required.
Anyone guess MateWonder why they are teaching to wire with a junction box method ?
Yes westward the switches are separate for two different lighting points, so i can terminate both switch cables into the JB ?Yes the loop line is the common live so if you have a two gang switch you could use one three core and cpc cable, one as the line supply from the loop terminal with a link at the switch and the other two for the switch line returns. If the switches are separate you will need two cables but just two cores with cpc.
Basically im cool with terminating power into the JB from CU, switch live for first switch, cable to lighting point, and loop out cable onto next lighting point, its the switch cable for next lighting point im stumped with !!!Yes the loop line is the common live so if you have a two gang switch you could use one three core and cpc cable, one as the line supply from the loop terminal with a link at the switch and the other two for the switch line returns. If the switches are separate you will need two cables but just two cores with cpc.