Hi there, my name is Paul and I'm currently studying towards a city and guilds level 2 electrical installation, we are currently on lighting circuits for our practical, we have been given a task to wire up 2 lighting circuits using a 6 terminal hager junction box, I'm ok with wiring one circuit from the supply in the box but struggling to get my head around wiring 2 from the JB, please excuse my ignorance with this but the tutor is not great at explaining things, I'm just struggling with where to terminate switch and light wires for 2nd circuit, and advice or even a wiring diagram would be highly appreciated, many thanks,

Paul .
 
What sort of Hager JB is it? Is it two separate circuits (one ocpd) or one circuit with two sets of switch lights? Doubt if you could achieve with the former.
 
Hello Paul welcome. We have a Trainee section on the forum. Go to the home page and see where you can apply for the Trainee section.
 
Hi there mate, it is actually 2 seperase circuits ?

Then common sense says they should be in two separate junction boxes.
There aren't enough terminals in a 6 terminal joint box to do this, each circuit will have permanent live, switched live, neutral and earth.
 
Then common sense says they should be in two separate junction boxes.
There aren't enough terminals in a 6 terminal joint box to do this, each circuit will have permanent live, switched live, neutral and earth.
This is what I was thinking, but the tutor showed us a completed one a pupil had completed in one of the previous classes and it was a mess with wires being connected with connector blocks as well ???
 
Hi there mate, it is actually 2 seperase circuits ?

This is what I was thinking, but the tutor showed us a completed one a pupil had completed in one of the previous classes and it was a mess with wires being connected with connector blocks as well ???

As has already been mentioned by @davesparks. 2 circuits into 1 junction box is not a good idea. You would have to put a sticker on the junction box stating it's being fed from 2 sources and both sources need isolating before doing any maintenance.
 
This is what I was thinking, but the tutor showed us a completed one a pupil had completed in one of the previous classes and it was a mess with wires being connected with connector blocks as well ???

Is this a training centre providing short courses by any chance?
 
As has already been mentioned by @davesparks. 2 circuits into 1 junction box is not a good idea. You would have to put a sticker on the junction box stating it's being fed from 2 sources and both sources need isolating before doing any maintenance.
Agree not an ideal situation, imagine testing for dead and only isolating one circuit, I know you should check everything, that's why I said it's not an ideal situation, especially if there are two OCPDs involved.
 
This is what I was thinking, but the tutor showed us a completed one a pupil had completed in one of the previous classes and it was a mess with wires being connected with connector blocks as well ???

I think we'd all like to see a picture of that and a copy of the actual question.
 
well.he should not be . we don't bite, except on Fridays. :D.
Hi there guys, not been scared off just yet lol no im studying towards city and guilds 2365 level 2, no its nothing to do with plumbing, what i will do is actually take a photo of the work, and also the page out of my practical tasks booklet city and guilds specify you have to do and then you can see if you can get your heads round it....im gonna ask the tutor on Thursday to explain what exactly is going on, because he does not make things clear at all and im getting pretty fed up with him because he is not teaching properly at all.
 
hi mate, it is two seperate lights from 1 circuit but both lights need a seperate switch ?

You only need a 3-way terminal block for that, as long as it's big enough.

You've got to get a picture of the attempt you've already seen, please! :)
 
When you say room do you mean space or enough terminals. You need the loop line, neutral, cpc and two switch return terminals, five required.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
WOLVERHAMPTON

Thread Information

Title
Wiring 2 lighting circuits using one 6 terminal junction box
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
67

Advert

Thread statistics

Created
Paul Langham,
Last reply from
Pete999,
Replies
67
Views
11,723

Advert

Back
Top