Currently reading:
ze tt
Discuss ze tt in the Electricians' Talk area at ElectriciansForums.net
mcm
Does the ze for a tt system have to be under 200ohms.
Did a reading today and it was 210ohms, the area that the rod is situated is next to a drain. When I got their the drain was over flown.
Would you say that the rod needs moving and replacing due to the position and the 210 reading.
From what you've said, yes, move it. Or add another one! theoretical maximum Ze is 1667 Ohms but (in GN3 I think) it states as a guide over 200 is not good.
I'd normally be looking in the tens (17, 27, 54) not the hundreds.
What installation is it?
We are given a maximum Ze for a 30 m/amp of 1667 ohms for a TT with a recomendation that it be under 200 ohms as you state,
210 ohms is not far off that recomended reading and I would consider that as acceptable
The resistance will vary depending on the weather,time of year,accuracy of test meter and in the end.it is an approximate reading of the resistance, which could well be lower if a earth rod resistance tester were used
Its location may well be a plus factor if the ground is being soaked
Many would accept readings that would be well in excess of your marginal result
I'd consider trying another area and seeing what you get, over flowing drain would of dropped the reading I imagin. Could well be much worse when the area dries out.
That or ensure the drain is always blocked!
Low figures are the aim,but its worth remembering,after every effort with urinating almost neat alcohol as failed (after having a gutsful of the rod and the beer)that the siuppliers earth electrode can be as much as 21 ohms,thats without the installation rod resistance and the earth conductor resistance
Low values and single figures are the exception rather than the norm, and is usually found because of a nearby Pme spike
GN3 states the earth loop test is permitted where there is an rcd, and resistances are relatively high, and precision is not required
Now that,with the other varying factors would encourage me to be content with 210 ohms
Either be content with that or get your drinking buddies to improve the readings :)
Reply to ze tt in the Electricians' Talk area at ElectriciansForums.net