OK, going to keep this short.

Supply is 150mm 4 core SWA, with NO supplymentary earth ( calcs done by others, )

QUESTION IS. Do you NEED to run an earth ( is it a regulation) from banjo on inside to earthing terminal inside board. Common sense and a simple ohms continuity test (0.01 ohms) says no. Just want people's thoughts on this.
 
Is the gland fitted into a gland plate?
Is the banjo fitted with heavy duty serrated washers to ensure good contact through any paint or the paint has been removed fully from the contact area?
Is the enclosure a 1 piece enclosure or segmented panelling which is screwed together?

If in doubt, tail it out!
 
Did common sense and simple continuity testing get a value of 0.01 ohms at a test current roughly equivalent to the PFC at the panel? A value of 0.01 measured with a multimeter with a sub-1A test current could be through a tiny spot of good contact which will pretty much melt instantly under the available fault current (which is presumably significant on that size supply)

In short, unless you have ensured a good high current connection to the earth bar by other mans then yes a suitably sized flylead is a damned good idea if not essential.
 
Reg 543.2.7...where the protective conductor is formed by metal conduit, trunking or ducting or the metal sheath and/or armour of a cable, the earthing terminal of each accessory shall be connected by a separate protective conductor to an earthing terminal incorporated in the associated box or other enclosure.
 
Did common sense and simple continuity testing get a value of 0.01 ohms at a test current roughly equivalent to the PFC at the panel? A value of 0.01 measured with a multimeter with a sub-1A test current could be through a tiny spot of good contact which will pretty much melt instantly under the available fault current (which is presumably significant on that size supply)

In short, unless you have ensured a good high current connection to the earth bar by other mans then yes a suitably sized flylead is a damned good idea if not essential.

The safety devices will open mate, the sheath will carry any fault currents that are generated, and the protective devices are 80kA. Don't want to go that route really, just want people's thoughts in the real world.

OK, so I m okay with with a 'fly lead' from banjo, so now what size?
 
The safety devices will open mate, the sheath will carry any fault currents that are generated, and the protective devices are 80kA. Don't want to go that route really, just want people's thoughts in the real world.

OK, so I m okay with with a 'fly lead' from banjo, so now what size?


Adiabatic equation and table 54.7
 
Last edited by a moderator:
Is the gland fitted into a gland plate?
Is the banjo fitted with heavy duty serrated washers to ensure good contact through any paint or the paint has been removed fully from the contact area?
Is the enclosure a 1 piece enclosure or segmented panelling which is screwed together?

If in doubt, tail it out!

Good answer like it.
No gland plate, no serated washers, 1 piece enclosure.
 
OK, that will equate to about a 6mm :)

Didn't want to go the abiabatic route, because an earth was not being taken back to source, as the the calcs state no supplymentary.


What's the PFC and what's the over current protective device?
 
No supply into the building yet, but the HV chamber is next door, so we are looking at Zs values of 0.01 by calculation, as we are top of the Tx
 
No supply into the building yet, but the HV chamber is next door, so we are looking at Zs values of 0.01 by calculation, as we are top of the Tx



Ok so you have calculated the Zs of the distribution circuit based on your assumed Ze of 0.01?
 
I repeat the HV chamber is next door, so from thr Tx the run is about 6 metres fed by 630mm parallel supply, so we can safely say that the impedance will be on 0.01. Again I repeat all this has been calculated and all protective devices have been designed to take fault current of 0.01 x root 3.
 
If and when you test it, you may have to introduce a fixed resistive component as the TX is so close that the resolution of your testers won't be able to measure it thus your reading will fluxuate wildly ;)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earthing inside a submain panel from main swa incomer
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
61

Advert

Thread statistics

Created
Guest 004,
Last reply from
Darkwood,
Replies
61
Views
7,764

Advert

Back
Top