I was installing a smoke and heat alarm on an existing circuit today (aico ei141 )was already in place, so I have used the same type for the install.
All insulation and resistance tests were within limits.
I interlinked the alarms and all worked then rcd tripped. Initially we thought it was a faulty hoover as the householder had just plugged in a hoover.
I reset and the rcd on the other circuit tripped.
it can cause either rcd trips they only trip when the smoke alarms are pushed into positon. I rechecked all the cables again(visual /insulation/ resistance ) and it still trips as soon as a smoke alarm is connected.
The only thing I can think of was the loft was full of stuff and I had to move some out the way to get access. It may have disturbed another circuit although, nothing trips until the smoke alarm is put into place.
I appreciate this is a shot in the dark I am going back tomorrow and would appreciate any advice.
The smoke alarms are on battery backup so the client is covered.
I also tried connecting the smoke alarms on another circuit breaker in case that was faulty.
Its still tripping even on their own circuit?
I am new to inspection and testing and wondering if there is anything else to try before going through every other circuit.
thanks in advance..... I hate getting beat.
Borrowed Neutral may be??
Interesting fault ... if it's not a borrowed N and since these units are not earthed (iirc) how can they be tripping RCD? Cable fault right at connector perhaps? Especially if you've tried the unit on its own circuit and it still trips RCD. What happens if you plug the new alarm into the original position?
Am I correct in thinking there is an existing smoke detector circuit from which you have installed a further two detectors? If so where have you connected the new ones from.
They are interlinked and I have visually checked them as well as muti meter test on that circuit.
basically live and neutral supply and then three core and earth between each alarm.
I disconnected my additional circuit and reverted to the original and it is still tripping. I think I may have physically disturbed another circuit and created a fault, although I cant understand why its only when the smoke detectors are connected the rcd fault occurs .
Just a reminder on IR testing - Aico installation instructions specifically warn not to do it with units connected. Likewise accidentally making the interconnecting link wire live will trash them, if I recall correctly.
I completed the ir testing with the cables unconnected from the smoke alarms. (the alarms were still in the box)Sad as it seems I actually tested each cable rather than link( R1-R2)as I had a new wander lead and it was a flat I was in.
So is the original circuit still in place and your new circuit is paralleled at the mcb?
Original cable which is direct from mcb was taken out from first smoke Alarm and is used as the live/ neutral /Earth supply in the loft void.
the interconnecting cables (three core and earth) for the alarms are linked in to this feed .
I will draw a diagram as I realise this explanation might not be clear
thanks for the help folks
EDIT: If it trips when you attach the smoke alarm - did you use the existing bases or fit new ones?
I tried it with brand new base and new alarm and it still trips. I stripped back the circuit to the original cable and new base /alarm and it still trips (ie back to original state). To say I am demented is an understatement. I appreciate that its hard to advise without being there.
I just wondered if I was missing something glaringly obvious
I tried it with brand new base and new alarm and it still trips. I stripped back the circuit to the original cable and new base /alarm ... To say I am demented is an understatement ... I just wondered if I was missing something glaringly obvious
Glass of favourite and the installation instructions, who knows? I've had domestic blindness more than once :)
Swap the N over to the other Nbar
How have you installed the 3 core and earth cable. Could you have possibly damaged(drilled/screwed) an existing cable located in the fabric of the property such as the wall?
Are you 100% sure you used the same cores in the interconnecting cable the same in each leg?
If you did IR at the board this wouldn't include the interconnecting cable so I suggest that you dis the smoke base and do IR across all 4 cores and see what comes back - and at the same time double check the colours and consistency.
It could be you have the L and N across 2 different RCDS I'm clutching at straws but worth proving a point, hence borrowed N
I understood you supplied the new detector straight from the CU
yes Murdoch I had checked using a wander lead for each cable at the different areas.
This was before connecting to any equipment.
I also visually checked the cable and connections as well in case of loose connection,... although any faults should have been picked up in the initial IR / test.
I cant understand how even reverting it back to the original circuit it now still trips.
All the new cabling can be seen as there are no cable drops for the new circuit and the only part that is hidden is the drop to the consumer unit (this is the original cable which was operating beforehand).
I am trying to help here!
So there was originally 1 smoke alarm, fed by T&E from the fuseboard.
You've added another smoke and a heat alarm to the existing smoke.
Now either 1 or the other RCD will trip.....
You've used 3 core cable for the new smoke & heat?
Or have I missed something?
apologies Murdoch if I seemed ungrateful I didn't intend to come across that way.
correct the supply is t&E from board then three core thereon
the third core is used for the interlink facility. if one alarm sounds they all sound together
I have drawn a very rough diagram I have left out the earth for clarity.
No offence taken!
Are you 100% sure you have the neutrals in the correct places in the smoke alarm bases
L
IC
N
No offence taken!
L
IC
N
yes mate I'm sure ...I checked three times or possibly four .That's why I took it back to the original circuit (T&E) to try and ascertain if it was a faulty unit to blame.
I checked with two base units and two detectors.
I couldn't understand why the other rcd tripped on two occasions though.
there was a lot of junk in the loft and I had to move some of it
I can only presume that somewhere I have maybe damaged another circuit ...but cant think if that's the case why it only trips when this circuit is made live and connected to the alarm..
What is the "new" cable run like? all clipped?
Still think you need to dis the new part and IR the new bit - and you must IR between ALL cores to make 100% sure.
Its all clipped in the loft area...
I appreciate what your saying. but I've disconnected the new part completely and the original cable, which was ok, is now the only part connected and its tripping the rcd !!!!
I disconnected it and IR tested that T&E as well
hence my headache !!!!
Next step, which seems a bit odd, but I think you should run the smoke from a new piece of t&e direct from the board at cu level. Do this to test the bases and heads you have.
You need to do this to rule them out of the problem ....
Sorry if I've missed something here but what is that other cable in the MCB? if the other RCD is tripping sounds like the crossed neutral. Just a thought but have you checked the two neutral bars are doing the corresponding MCB bank.
He has yet to clarify how it is connected and which parts are new and what is existing.
The other cable is lighting circuit for hall.
However I have tried the smoke alarm cicuit in the adjacent mcb on it's own.
As stated by you and others I will double check the neutral bar in case there is a crossover or borrowed neutral.
Glasgow
rcd tripping after smoke alarm fitted.
DC-backfrom the past,
Midwest,