In a standard set up for emergency (non maintained) lighting ,in an HMO for example, is it necessary for the lighting to form a single circuit i.e to be simultaneously isolatable for testing purposes or can each light be fed separately with its own test switch?
 
Nowadays you can get emergency lights with a test switch built in. Also Cosnic do emergency control gear with built in self test. But one switch to bind them all is ok, the only problem being is you can't see the lights on other floors when you use one switch. So quite often it is one switch per floor.
 
You can have one test facility or individual. The main criteria is that non maintained fittings operate upon failure of the associated general lighting circuit. For example if you have a non maintained fitting in a corridor it must illuminate upon failure of the general lighting in that corridor.
 
Nowadays you can get emergency lights with a test switch built in. Also Cosnic do emergency control gear with built in self test. But one switch to bind them all is ok, the only problem being is you can't see the lights on other floors when you use one switch. So quite often it is one switch per floor.

Apols for laziness but do you know who makes them?
 
Who is going to do the monthly test? In the flats I look after, the maintenance man does the monthly test. I think he wouldnt be too amused at having to drag a pair of steps all over 5 blocks of flats and turn off multiple test switches.
One switch off, check they work, sign the book and move on.

Any faults and the annual 3 hour tests are done by yours truly.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South East
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Emergency lighting BS 5266
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
South Spark,
Last reply from
Taylortwocities,
Replies
5
Views
1,855

Advert

Back
Top