Perhaps it is to dissipate a static charge? I don't think it's a requirement in the regs but it's certainly not a bad idea.
Remember, if it's a PME system then it will need a seperate earth rod.
why? the separate earth rod for everything PME is not true!
Where else could you bond it to? You can't take it to the PME?
why can it not be taken to the PME?
Because you would be taking the PME outside of the equipotential zone. You would need electricity board permission and in my experience they are reluctant to give you an answer.
the airel is not going to introduce another earth potential to the installation. plus you do not need board permission to export a PME earth. they prefer it if you dont but it is simply up to yourself.
I was told something completely different by my NICEIC inspector. He pulled me on a garage/studio conversion that I installed a few years ago and said that I should have installed a seperate earth rod. He wasn't impressed either....
Perhaps it is to dissipate a static charge? I don't think it's a requirement in the regs but it's certainly not a bad idea.
Remember, if it's a PME system then it will need a seperate earth rod.
I was told something completely different by my NICEIC inspector. He pulled me on a garage/studio conversion that I installed a few years ago and said that I should have installed a seperate earth rod. He wasn't impressed either....
The bonding should be taken back to the pme...the purpose of main bonding is to ensure there can be no potential difference between conductive parts and extraneous conductive parts....introducing another earth potential via a rod would totally defeat the object of the excercise.
that is the point i was trying to make. people blindly go around banging in spikes because they see PME.
The bonding should be taken back to the pme...the purpose of main bonding is to ensure there can be no potential difference between conductive parts and extraneous conductive parts....introducing another earth potential via a rod would totally defeat the object of the excercise.
Even for equipment outside of the equipotential zone?
Why would you want to bond something outside the equipotential zone?![]()
I like this topic also.
The fact that the aerial will now act as a huge lightning conductor opened my eyes.