If something is REQUIRED then that would mean that you MUST use DP rcbos when using an up front rcd, but that's not the case as there are other options to having to use dp rcbos.In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
I have never stated dp rcbo's MUST be used where an upfront rcd is in service, if you read back through my posts I clearly agree other options are compliant such as a dual rcd board.If something is REQUIRED then that would mean that you MUST use DP rcbos when using an up front rcd, but that's not the case as there are other options to having to use dp rcbos.
Meaning that it's not a requirement.
You said There is no specific regulation stating that a dp protective device is required for a tt with an upstream s type rcd.I have never stated dp rcbo's MUST be used where an upfront rcd is in service, if you read back through my posts I clearly agree other options are compliant such as a dual rcd board.
What I do state (very clearly I believe) and stand by is that wherre rcbo's ARE used......they must be dp where there is a upstream s type rcd and in that arrangement are effectively a requirement, you seem incapable of understanding that I am only refering to where rcbo's ARE used. I believe i have been quite clear that with other arrangements sp rcbo's are compliant.
Perhaps you would be good enough Mainline to answer this.
Lets say you have a job where the designer has specified DB's with rcbo protection to all final circuits. A main switch of s type rcd is also specified. Its a TT earthing system.
Would you install sp rcbo's and provide an EIC on completion?


Unfortunately you have chosen to ignore the fact that I am only referring to a situation where an up front s type rcd is used with rcbo final circuit protection, a common arrangement but not the only one. In that case sp rcbo's are not compliant. At no point have i suggested other compliant arrangements are not possible.You said There is no specific regulation stating that a dp protective device is required for a tt with an upstream s type rcd.
Which was my point from the start.
That it’s Not a requirement.
@westward posted the same statement as I was typing saying dp rcbos aren’t a requirement and your reply was yes they are and proceeded to try and find a situation where they would be an actual requirement which has now come down to a designer telling you to fit them
You can go through all the scenarios you like where the use of them is going to be the sensible thing to do but That would still not make it a requirement.
If a main switch rcd is within the enclosure I would be questioning the competence of the designer
why would I say that they were compliant when they are not ?Unfortunately you have chosen to ignore the fact that I am only referring to a situation where an up front s type rcd is used with rcbo final circuit protection, a common arrangement but not the only one. In that case sp rcbo's are not compliant. At no point have i suggested other compliant arrangements are not possible.
Clearly you have not answered my question because you know you cant without admitting that for the specified arrangement sp rcbo's not compliant.
You can but it is not good design practice. It also depends on the cable between the CU and the outdoor blocks:The question is, if I get the main CU replaced with 10 RCBOs gather this will impact the outdoor RCDs?
Or can I have an RCBO and RCD on the same circuit?
Why?I'd hate to spend all the money on a new CU and end up with the odd MCB within it.
No cross bonding required if rcd protected.One more....
My gas mains is earth bonded with a 10mm cable, this is near the CU (understairs cupboard).
Can the water (hot/cold) and heating flow pipes be cross bonded (interlinked). This cross bonding would happen under the comobi boiler with is not near the CU.