hi all,

What are your thoughts on how the 6231 cables been terminated? Will aluminium cause eddy currents? Thanks
 

Attachments

  • IMG_3857.png
    IMG_3857.png
    2 MB · Views: 378
  • 94BE07C3-3A22-4AC2-AAC2-C94A3D88BD5A.jpeg
    94BE07C3-3A22-4AC2-AAC2-C94A3D88BD5A.jpeg
    302.2 KB · Views: 233
Yes aluminium is a good conductor, so eddy currents will be greater than if it were steel.

Whether in practice anything bad could happen I'm not sure
 
There might be some eddy current effects but far less than for steel (or anything other exotic material that is ferromagnetic). See 521.5.1 for that.

Ideally you always would take the whole set through a single hole, it also helps preserve circuits when several are present so less connection errors (i.e. L1-3, N & E kept to same MCB, etc, etc) than if they are going via different holes.
 
Unless I'm very much mistaken the issue of eddy currents only materialise in ferrous materials. Gland plates are often made of aluminium where large singles are brought into an enclosure.
Seems I am mistaken - thanks 🫣
 
  • Like
Reactions: nicebutdim
The first picture I assume is steel in which case it is wrong. The aluminium panel in the second picture is fine but the lock nuts assuming they are steel are not.
 
  • Like
Reactions: nicebutdim
Seems I am mistaken - thanks 🫣
You are not mistaken, eddy currents (Foucault currents) will be induced in any conductor within the presence of a changing magnetic field.

However the ferrous material tends to enhance the effect.

I have to say though, we designed MV and HV switchgear for typical currents of circ 630 - 3000 A and using 1/4" steel plate we used separate apertures for each phase, and only added around 5-10 deg C temperature rise!

So in my opinion it doesn't matter at all whether the cables go through the same hole or different holes.

However if it is ferrous material, regulation 521.5.1 mandates that all current carrying conductors go through the same hole.
 
Has anyone found much difference in temperature when it’s only the CPC which goes through a separate hole? Line and neutral conductors going through together.
 
Has anyone found much difference in temperature when it’s only the CPC which goes through a separate hole? Line and neutral conductors going through together.

Won't add any heating effect, unless it is carrying current.
 
From memory though doesn’t the reg also say “and the appropriate earthing conductor” should enter through the same hole?
 
  • Like
Reactions: nicebutdim
I have to say though, we designed MV and HV switchgear for typical currents of circ 630 - 3000 A and using 1/4" steel plate we used separate apertures for each phase, and only added around 5-10 deg C temperature rise!

This is interesting, but I believe the eddy current problems get worse the thicker the steel gets.

The eddy currents become an issue if the conductors don't just pass through separate holes but also separate couplers or even conduits.

I've been meaning to experiment with this for a while, maybe I'll get some time in the workshop soon.
 
I've been meaning to experiment with this for a while, maybe I'll get some time in the workshop soon.
I hope you have many 100's amps available in your workshop!
From Mr Ward rather a long time ago:
 
Beat me to it :)
 
Snap 🤪
And other words..
 
I hope you have many 100's amps available in your workshop!

Nope, and shouldn't need much current either.

I recall Lucien mentioning that he made a simple square of conduit with a lampholder in the middle of one side and a mains input opposite it which got very warm with the live routed through one side and the neutral through the other with just a 100W lamp in it.
 
Nope, and shouldn't need much current either.

I recall Lucien mentioning that he made a simple square of conduit with a lampholder in the middle of one side and a mains input opposite it which got very warm with the live routed through one side and the neutral through the other with just a 100W lamp in it.
Not borne out by John Ward's video, or Julie's experience. I'm just perplexed now!
 
  • Funny
Reactions: nicebutdim
Yes it does, I think this is down to the fact a lot of current can flow through it under fault conditions.
I guess the other side of that is it might add some impedance to the system due to inductance, making the AC R2 a bit higher than the DC one measured during dead testing to verify conductors are properly speced and installed.
 
Just annoying when you’re a bit of a neat freak with a distribution board and know that taking the earths through their own hole at the top of the board makes it look so much better 😅
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
gloucetser

Thread Information

Title
Eddy current clarification
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
dave992,
Last reply from
Mike Johnson,
Replies
37
Views
5,770

Advert