Eddy currents are a real thing, I have seen several instances of damage by them.
The worst case was on the LV box of a 2MW transformer, four conductors per phase all neatly grouped by the phase and taken through a steel plate. The paint on the plate had burnt off around the cables and discoloured the steel. We changed the gland plate to brass to solve the problem. Interestingly at the other end the singles were again taken through steel into the switch board but there was no sign of heating, I think this was due to the singles being taken in randomly rather than bunched in phase groups.
As said above there will always be induced currents from singles but it is much worse if they pass through ferrous metal. In another case we had four singles passing through a steel plate, again there was signs of heating. This was solved by cutting a slot to link the four holes (which were in a line) then brazing it shut again to retain strength. The brass in the brazed joint was enough to prevent further eddy current damage.
 
Eddy currents are a real thing, I have seen several instances of damage by them.
The worst case was on the LV box of a 2MW transformer, four conductors per phase all neatly grouped by the phase and taken through a steel plate. The paint on the plate had burnt off around the cables and discoloured the steel. We changed the gland plate to brass to solve the problem. Interestingly at the other end the singles were again taken through steel into the switch board but there was no sign of heating, I think this was due to the singles being taken in randomly rather than bunched in phase groups.
As said above there will always be induced currents from singles but it is much worse if they pass through ferrous metal. In another case we had four singles passing through a steel plate, again there was signs of heating. This was solved by cutting a slot to link the four holes (which were in a line) then brazing it shut again to retain strength. The brass in the brazed joint was enough to prevent further eddy current damage.
I always thought they had the same effect on brass as I was once told brass bushes wouldn’t prevent the issue or is that because the brass bushes are drilled and fitted to the steel casing of a distribution board?
 
would not a brazed up slot still count as a shorted turn of a transformer os sorts?
It is conductive but not magnetic. The braze stops the magnetic circuit and forces the magnetic flux from all the cores to go around all four cores. The sum of all the cores should be zero so there is no magnetic flux left to induce currents.
 
always thought they had the same effect on brass as I was once told brass bushes wouldn’t prevent the issue or is that because the brass bushes are drilled and fitted to the steel casing of a distribution board?
You are correct. Brass bushes in a steel plate will not make any difference. You have to look at the magnetic circuit, all the cores have to pass through the same hole in any ferrous material.
 
I thought any conductive material in a moving magnetic field will induce a voltage.
Magnetic flux is a thing but it's the moving flux or conductor moving though a magnetic field that induces a voltage.
I was also taught that below 100 amp current is unlikely to be a concern.
Having said that I bring all my conductors in thought he same hole in a metal enclosure.
 
I thought any conductive material in a moving magnetic field will induce a voltage.
Magnetic flux is a thing but it's the moving flux or conductor moving though a magnetic field that induces a voltage.
That is correct, A changing magnetic flux will induce current in a conductor, but by putting all the cores through the on hole in a ferrous material the magnetic fluxes cancel out, hence no induced current.
If the cores are brought through separate holes in a ferrous material each will induce a current. These currents will summate/negate and produce losses which can result in hotspots. I agree with a comment above that below 100A there will be no heating, But it is still an inefficiency.
 
I remember working at the large Debenhams in Manchester city centre and they had installed a new sub panel in 600.0 singles on a tray. They entered the existing panel through separate entries of the ferrous panel and it was buzzing like crazy but there was no heat build up.
 
I remember working at the large Debenhams in Manchester city centre and they had installed a new sub panel in 600.0 singles on a tray. They entered the existing panel through separate entries of the ferrous panel and it was buzzing like crazy but there was no heat build up.
Surely my 1.5mm and 2.5mm earths going through their own hole will be OK then? 😂

Complete opposite end of the spectrum!

Wonder if my NIC inspector would have hard feelings about it
 
Last edited:
The first picture I assume is steel in which case it is wrong. The aluminium panel in the second picture is fine but the lock nuts assuming they are steel are not.
Hi i dont know if this is the right place for this question here goes, can eddy currents be used to to 8dentify diffrent metals? Tia.
 
Just annoying when you’re a bit of a neat freak with a distribution board and know that taking the earths through their own hole at the top of the board makes it look so much better 😅

Whilst neatness is important you should not be putting form over function.

Putting all the earth's through a separate hole might look neat but it can make the next person to work on that boards job a lot harder.
 
Hi i dont know if this is the right place for this question here goes, can eddy currents be used to to 8dentify diffrent metals? Tia.

I imagine they could, but it doesn't seem an ideal method of identifying materials. The process would require the possession of quite a bit of information and strictly controlled conditions.
 

Reply to Eddy current clarification in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On a domestic Cu 60 amp would live and nuetral tails cause eddi currents of any significants if the tails were run in sperate metal conduit but...
Replies
4
Views
699
Hi all. I am installing some metal trunking vertically in a meter cupboard to contain all the meter tails for an apartment block. I have 5 sets...
Replies
1
Views
639
Hi Guys Been asked to install Eddi & Harvi units, for TP new build we're just finishing off. PV inverter is down in basement plant room right...
Replies
1
Views
898
I never did like transformer theory in my degree course and that was 40 years ago. I'm a boat builder now and we tend to have big battery banks...
Replies
3
Views
1K
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
414

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock