T

trickyb

Hi been asked to fix fire exit sign over door for emergency light (non maintined) am i right in saying this would need a designated ciurcuit to it from the consumer unit ? cant seem to find info in the osg :thinking:
 
As far as i believe it would need to be fed from one of the local lighting circuits in that area and in a cable of the same type, so that if the lights fail in an area you will lose power to the asscociated emergency lights and if there is a fire condition the cables will fail at the same times as well
 
Last edited:
If it is a maintained fitting then it can be fed direct for the DB via a test switch if it is not it should be fed from the local lighting circuit again via a test switch.
 
If it is a maintained fitting then it can be fed direct for the DB via a test switch if it is not it should be fed from the local lighting circuit again via a test switch.
if it was maintained or non maintained you would need a test facility so i would also fit the keyswitch upfront at the DB
 
geordies saying own cuircuit othes saying fed of local lighting cuircuits? Have i put a cat in amongst the pidgeons ? lol :thinking::20:
Look at it 1 way, i am taking it is a commercial installation, 1 local lighting circuit fed from say 1L1 and you bring your exit sign to the same area and stick it on 1L2, power cut on L1 and you lose your general lighting but your emg light is siting nicely on non-maint giving off no light with people staggering around snapping legs, or in a single phase view same setup again with a bit of damage given to your new emg light circuit which causes the MCB to operate (un-noticed as nothing else goes out), Ethel the manager does not notice the charge indicator failed, powercut again and possible carnage ensues.

Just my view, draw your own opinion, :83:
 
Local circuit and I always take it via a key switch to enable testing, without having to isolate the entire circuit.

Local circuit fails and the EML comes on simple. Even a maintained one will be taken from a local circuit too, but will have both switch and perm lives.
 
definately a local circuit and if the circuit doesnt have a key switch to test the emergencys put one in local to the area where the em light is dont understand why people are saying it has to be a new circuit, aslong as the circuit your adapting is safe (test first) and you have a permanent feed happy days
 
definately a local circuit and if the circuit doesnt have a key switch to test the emergencys put one in local to the area where the em light is dont understand why people are saying it has to be a new circuit, aslong as the circuit your adapting is safe (test first) and you have a permanent feed happy days

Must be the mince pie intake still taking effect
 
You need to consider what the light is intended to do.
Some installations such as Cinemas, Theaters or even Night clubs require emergency exit signs to be lit whenever the installation is being used.
Other installations only require the light to be lit in the event of a power failure.
Other's again only require the light to be lit in the event of a fire.
In most cases, feeding the light off of the locall lighting circuit rather than a dedicated circuit is preferable, as it will light up on battery if that local circuit fails, rather than wait for the whole installation to fail.
 
BS5266 does not specifically tell you where you can and cannot feed a self-contained emergency light from.

You can feed the light from where ever you like.

All that matters is the emergency lighting operates upon failure of the normal lighting.

In my opinion the sensible solution is to feed the self-contained emergency lighting from the same MCB/fuse (via key switch) which feeds the normal lighting in that area.
 
Last edited by a moderator:
Ther's no real need for a key switch, as testing can be achieved through switching off the relevant MCB.

It would make duration testing of the emergency lighting very awkward.

Say if it was schedule to be done late one day and its dark outside, you don’t want to lose your normal lighting, especially if the school is occupied.
 
Last edited by a moderator:
Ther's no real need for a key switch, as testing can be achieved through switching off the relevant MCB.

Just found this:-

BS5266-1:2011 8.3.3

Each emergency lighting system should have a suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply)
 
Last edited by a moderator:
This looks to be an old document as it does not mention The Regulatory Reform (Fire Safety) Order 2005 which supersedes a lot of the legislation mentioned

Yeah just had a look, it’s really really old.

BS5266-1:2005 was revised in December 2011, Superseding BS5266-10:2008 as well.
 
Last edited by a moderator:
Just found this:-

BS5266-1:2011 8.3.3

Each emergency lighting system should have a suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply)

The problem I have with such a method, is that would not show whether the Lux levels are sufficient. Only by interupting the normal supply could that be assessed.
 
The problem I have with such a method, is that would not show whether the Lux levels are sufficient. Only by interupting the normal supply could that be assessed.

I normally if say i have a local grid switch with one key a one switch my load from the key would also feed the switch so i am not interupting the normal supply to areas not on test
 
Just got this last year from the NICEIC stating it was new and just released by the BSI, been well had over, good of the nic knocking out their old crap along with the old PIR's

well miffed

Sorry my mistake, I’m getting my years mixed up.

BS5266-1:2005 was superseded in December 2011
 

Reply to fire exit sign in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock