I have to put 25 led down lights in a garage , customer wants them all on one switch line which will be 100 metres long. I'm going to use 1mm. Should I break them down into two lots of 14 ?
 
Give more info
What kind of fittings?
Mcb rating(s)?
Volts drop if common driver unit may be an issue if 230v to lampholders still at 100m id be calculating it although you have other hurdles to get over before this


What voltage- If gu10 you must load calc them for the maximum lamp value i.e. 50watt , also a led lamp has an inrush you will be limited to the no' you can switch on at anyone time on the same mcb its to be noted that led lamp will have a DC driver inbuilt so an inductive load with a inrush on power up.
 
Last edited by a moderator:
the startup current on LED lamps can be rather high !

id split the lamps on two circuits then wire them back to a single double pole contactor and then switch the contactor with the 100m switchline run.

once you've done your cable calc for the 100m run you will probably find a 1.5mm will be sufficient or a 2.5mm for luck ! lol
 
I'm with shocking on this one ! No I can't be bothered into going into the workings outs calcs wise, but 2.5, will be good through a contactor, and it will easily fit into the switch too !
 
the startup current on LED lamps can be rather high !

id split the lamps on two circuits then wire them back to a single double pole contactor and then switch the contactor with the 100m switchline run.

once you've done your cable calc for the 100m run you will probably find a 1.5mm will be sufficient or a 2.5mm for luck ! lol

The startup current on SOME LED lights can be high. Others are very well behaved. I wouldn't go to the expense of splitting the circuit or adding a contactor without finding out the characteristics of the proposed lights.
 
Really ?????
Use triple pole switch or double pole , split ccts into rows , 10A type c mcb, jobs a gooden!

No need for 2.5s or contactors.
 
Last edited by a moderator:
Why is this switch line 100m long anyway?

Depending on the overall configuration of the circuit, you might be running into problems with volt drop (as mentioned before) or Zs, depending on the length of the supply cable and the rating and power factor of the lights.
 
Without more input from the OP this thread can't go any further we just don't have the info and all the speculation may be just a waste of time ive reserved my comments until we know more .... until then we might as well play it safe and use 6mm over 3 circuits and save any calcs etc ;)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

growler

Arms
-
Joined
Location
Basingstoke

Thread Information

Title
100m switch line
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
growler,
Last reply from
Darkwood,
Replies
16
Views
2,699

Advert

Back
Top