A lamp is unlikely to cause an overload as it will tend to blow very quickly if much of the filament is shorted out, so in one sense it's a fixed load. But certain types of lamp, especially small powerful halogens, can flash over inside the bulb as the filament breaks and draws an arc. To control the damage the lamp maker will specify a maximum fuse or MCB rating and curve, to limit the let-through in the event of violent lamp failure.
I have been standing next to a Par 64 that had a lamp flashover when protected only by a B32 and it was like a cannon being fired - A singing arc for about 1/2 second followed by a huge flash and bang and broken glass and quartz shot out of the front all over the room. A linear is unlikely to do this because the terminals are so far apart but still I would respect the manufacturers' fuse specs.