L
Leesparkykent
Out of interest what's most commonly used?
Even if you halved 1mm's ccc (method C), it would still be 8A.1mm unless there is loads of Insulation surrounding my cables e.g. Celotex, Kingspan
1.5mm2 don't know what Shirley usedShirley (!) you use a cable suitable for the design, not 'cos of its physical size?
If it satisfies the design then using size as a consideration is legit Shirley ?Shirley (!) you use a cable suitable for the design, not 'cos of its physical size?
If it satisfies the design then using size as a consideration is legit Shirley ?
I use 1.0mm almost exclusively, and the reduced size helps considerably on most rewires. Never have a problem with design considerations.
Possibly ?Me thinks you misunderstood my post?
Even if you halved 1mm's ccc (method C), it would still be 8A.
Sure about that ?
I think 6A is the most onerous ref method in the OSG for 1.0mm
I'm misunderstanding yours now![]()