Murdoch, surely there will be adequate protection against shock if the electric circuit is protected by the RCD?
 
Murdoch, surely there will be adequate protection against shock if the electric circuit is protected by the RCD?

There will be adequate protection by RCD, IP and double insulation, absolutely nothing wrong with this setup but we still fit inline extract, such a better job!
 
It should state clearly in the Installation instructions which zones it is suitable for. The manufacturers instructions take precedence over any rules and regulations.

Cheers..........Howard
 
Have just accessed the manufacturer's instructions. All it says is that the wiring must comply with current IEE Regs. The fan is Vent-Axia Lo-Carbon dMEV Unit, IPX4 rated, 240V, and located in zone 1. Just to repeat, the cirucit is RCD protected (actually, RCBO in my case).

My original question still stands: can I keep this fan, or must it be replaced with a 12V one to make it satisfy the regs?
 
it wont be alot more to just buy a 12v why cant you take the 230v back and exchange it? seems mixed opinions and it might be less hassel in the long run for you so you can get it signed off!
 
Have just accessed the manufacturer's instructions. All it says is that the wiring must comply with current IEE Regs. The fan is Vent-Axia Lo-Carbon dMEV Unit, IPX4 rated, 240V, and located in zone 1. Just to repeat, the cirucit is RCD protected (actually, RCBO in my case).

My original question still stands: can I keep this fan, or must it be replaced with a 12V one to make it satisfy the regs?

Keep it if you want.
It complies with the regulations as long as it's IPX4 or IPX5 if there's a chance of water jets hitting it.
Tell your electrician to check table 8.1 in the OSG.
 
Have just accessed the manufacturer's instructions. All it says is that the wiring must comply with current IEE Regs. The fan is Vent-Axia Lo-Carbon dMEV Unit, IPX4 rated, 240V, and located in zone 1. Just to repeat, the cirucit is RCD protected (actually, RCBO in my case).

My original question still stands: can I keep this fan, or must it be replaced with a 12V one to make it satisfy the regs?

Toad, on a forum, you get a mixture of fact and opinion.

The facts are that the fan by way of it's IP rating does comply, it's also double insulated and RCD protected so if you want to keep it there, you can.

The opinion is that an inline fan or SELV unit is better but seeing as your fan is fitted and working.....
 
didnt the elctrician fit the fan? if not whys he signing off someone elses work? if he wont budge and its correctly rated just remove the fan and refit after its signed off or get himm to mention it in the observations that he refused connection.
 