I'm planning to install 4 50 watt LED flood lights and three PIR's the idea is to link the switched output of the PIRs so if one is activated all of the lights come on. I also plan to link the switched output to a wall switch so that the customer can turn them all on manually.

It is possible that just one PIR is activated so all of the current will be running through the one PIR. I have read somewhere that LED floods have a high start up current.

If I use PIR's rated at 1000 watt incandescent and 500 watt fluorescent will that be ok ?

Thanks
 
should be fine. you could always parallel the PIRs to a 4 pole contactor and use 1 pole for each light.
 
Probably will need a contactor for example the Time guard SLB2300 Stand alone PIR can handle 2300W incandescent, 500W fluorescent/low energy or 140W LED.

You may be able to find a PIR with a higher maximum LED load rating or swap the 50W floods for 30W if the design permits or install a contactor.

tgpir.PNG
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Lyme Regis
Business Name
Current Energy Solutions

Thread Information

Title
4 x 50 watt LED Flood Lights on 3 PIR's
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Stuart Houghton,
Last reply from
Leesparkykent,
Replies
3
Views
1,381

Advert

Back
Top