I install a/c but not clear where an EIC would finish. On the simple split systems where an electrician provides an isolater for the outdoor unit. This is easy to de-mark, test and certify to BS7671. However the supply to the indoor unit, power and comms is often derived from the PCB of the outdoor unit and as such is derived supply. YY cable is often used for this as it is ideal having the extra core(s) and is small enough to terminate in the indoor unit.
The indoor units i have come across have all been 240V supply and you get defintely get a belt off this YY cable.
On the installation checklist there is an area when you certify all electrical connections are done to Mis (usually specifying ferruled terminals) but thats it, you certainly would not IR test the cable when connected and your EFI tests are i think impossible to ascertain as the supply is derived off the PCB with protection systems for overload and short cct.
In the MIs there are no electrical tests as we would know it, you basically terminate the cable correctly and thats it.
On VRF / multi systems, it is different as an FSU is needed for each indoor unit and there is just a comms cable similar to ethernet that connects them together, so its easier to do an EIC for the outdoor unit and each indoor unit to the FSU.