London uses a solid LV network I think it is the only part of the UK to do so. Bit difficult to explain but basically you have about four transformers with HV and LV protection feeding into a solidly interconnected area. Better utilization of copper but very high fault levels, most faults blow clear but can cause a very big bang.

Are you talking about a network system like Manhattan, Brooklyn and Queens?
 
I have no idea what you do in the colonies.


Is this system, or like it, used in London?

1597607182411.png


Another example:


1597607261276.png
 
Fascinating differences. How many kva is your 11kv-415 volt transformer?
I don't really know the range, but I think most built up areas have ones in the 500kVA to 1MVA range feeding something like 100-200 homes.

Remote building, farms, etc, probably have ones in the tens of kVA region depending on their needs, but the majority of UK supplies would be in modest-sized networks around a middle-sized substation.

Hopefully others on here with far more DNO knowledge can comment?
 
I don't really know the range, but I think most built up areas have ones in the 500kVA to 1MVA range feeding something like 100-200 homes.

Remote building, farms, etc, probably have ones in the tens of kVA region depending on their needs, but the majority of UK supplies would be in modest-sized networks around a middle-sized substation.

Hopefully others on here with far more DNO knowledge can comment?

500-1000kva seems like a fair size.
 
Wow - it give me the willies just thinking about working on something like that!
Now think about doing it in a small space, with everything around you made of steel, and rolling about at sea ... and oh yes, DC o_O
You don't got your MV cables in switch loops like Germany (1:00 as an example)?
I struggled to spot the details as they zoomed in and out of stuff a bit quick. But yes, out here in the sticks it's normal to have loops. I happen to know that we are fed from 2off 132kV feeders into the substation the other side of town. Those feeders go into 132/33kV transformers and 33kV distribution boards. Then a number of 11kV boards are fed from 33/11kV transformers. Having had a private tour of the new 11kV distribution board before it was commissioned, a typical arrangement has the board in two halves - each fed from the separate 132kV feeders via the 33kV system. There's a link between the two halves, so that a loss of one of the feed can be catered for by opening the feeder and closing the link - otherwise it's left open.
Then for the local network, it's typical to have an 11kV ring that goes from a breaker on one side of the board, out in a loop round a few 11k/415V substations, and back to a breaker on the other half of the 11kV board.
The 415V substations will be connected with ring main units - two switches or breakers connecting to the two directions in the ring, and a third for the transformer. Somewhere around the ring, a switch will be left open so that it's running as two radials - but if there's a fault, switches can be opened and closed to feed part of it from the other end. Going back just a decade or two and thes were all manual - so needing an engineer to drive round to operate them. They've been upgrading over the years to add more remote switching so the controll centre (dwon in Manchester for us) can clear (or partially clear) more faults.

Then as already mentioned, depending on the layout, some of the local distribution network has the ability (by fitting/removing links) to be fed from more than one substation.
At my last job I recall watching as a couple of DNO vans pulled up at the substation across the road. One of the guys walked round the corner out of site and then the lights dimmed a little - I recall me and my manager looking at us with that "are the lights going to go out" look. They then pulled the fuses from the output side of the substation and proceeded to do some maintenance on it - sucked the oil of of the breakers, did some work inside (I gather they have had some problems with bad joints), then refilled with oil. When they finished, a guy went round the corner, and the lights went back to normal. The logging from our UPS showed a 10 to 20V drop in voltage while they were working.

As an aside, one of the experiments the DNOs have been doing on load/supply management has involved deliberately linking busses (e.g. the 33kV busses in the above example substation) in main substations and altering transformer taps to create circulating currents. In effect, using the distribution network as a large heater element to deliberately waste energy - just as a very short term measure to compensate for a surge in supply (those darned renewables) or a sudden loass of a large load.
Dunno what came of that.
 
Cookie
Sorry for the delay in answering, yes I think the London system is similar to the drawing you posted. I have never worked on that system only read about it.
Re backfeeding substations, the system is usually designed with 30% of the capacity available via backfeeds this is so that the substation can be switched out for maintenance on a summer day. If the load is greater than the available then the lights get dimmer as per Mr Ohm.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Earth

Thread Information

Title
Are DNO cables fused?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
56
Unsolved
--

Advert

Thread statistics

Created
Cookie,
Last reply from
R-fur,
Replies
56
Views
7,424

Advert

Back
Top