Pre empting my 2382 and trying to calculate lb so as I can calculate voltage drop.

Circuit I have used for this is an upstairs lighting circuit, 1mm2 t&e 4 light points and length of approx 19m.

Cable installed to ref method C.

Getting myself a bit confused but this is what I think I should be doing:

Using the OSG app 5 table 1a I assume a load of 400 watts, 1.818A.
Is this actually lb or should I apply diversity?
 
Apply diversity, apply de-rating factors, such as insulation, ambient temp, 3036 rule etc, that will give you your IB then MV/M/A x IB x L / 1000

Sorry don't have osg or brb with me to work out any examples for u
 
use worst case scenario. design for max. loading. i would round off Ib to 2A, then calculate volt drop from that. just makes it easier all round. if you want to allow for future expansion , though, allow for an extra point or 2. i.e. 600watts, 2.6A, round up to 3A.
 
So do I round up to 2A then apply 66% diversity?
Cable is either direct in plaster (from CU to loft) or clipped direct to joists in loft, at each lighting point the cable passes thru approx 400mm of plastic conduit to keep insulation from direct contact, is ref method C correct for this?
Do I assume ambient temp to be around 20•c for a domestic property, that's what we normally have the stat at on the heating?
Protective device is 6A type B mcb so does 3036 apply?
 
3036 only applies to bs3036 rewireable fuses.
 
Thought so.

What you say about worse case makes sense to me but does that mean I should not apply diversity as that would lower lb?
 
Thought so.

What you say about worse case makes sense to me but does that mean I should not apply diversity as that would lower lb?

Yup IB after application of diversity and application of appropriate de-ration factors, sorry for the bum steer regarding 3036's I should have explained further, my apologies it only applies to semi enclosed bs3036 fuses and is a value of .75
 
unless of course this is an exam question in which case dont go wandering with your figures give them what they are asking for :)
 
Nope not exam, my own house and using it to try and pick up this stuff.
Will do calcs and put them up in a while.
 
Cool mate give us the figures and your workings out and one of us will give it the once over
 
One last thing, is my ref method quoted correct for the installation described.

No bum steer Hightower, it keeps me on my toes!
 
Here goes-

4 lighting points on circuit assumed at 100W each gives 400W or 1.818A.

Applied diversity of 66% gives 1.199.

Ambient temp of 20•c correction factor of 1.04
1.04 * 1.199 = 1.246.

Mv/A/m for 1mm2 conductor with ref method C = 44
Lb = 1.246
circuit length = 19m

Voltage drop -
(44 * 1.246 * 19) / 1000 = 1.041
 
Thanks mate, is there anything else I'll need to calculate?
I know I have to do final ring cooler etc but is it just v drop and ensuring csa is suitable after corrections?
 