Hello everyone and HNY.

I need clarification on this:

I been asked to change the fuse board in commercial premises, it is a sub main SP board in a basement area. The earthing cable/cpc to board is the armor of SWA cable, all circuits to the accessories has the cpc via metal conduit. I had a look at the job and the only tests I could do is Zs. The readings where in the range of 0.40-0.50 ohms, so it seems that I have fairly good Ze and R1+R2 (still to be confirmed when the isolation can take place)

I know that for new installs, you cannot have the armor or conduit as the only means of cpc, but it is only the board change and all wiring methods complied with the regs when they were installed.


So, the question is:

· Do I have to pull a new earting cable/cpc up to the board and,
· Do I have to pull in the cpc for all wiring in the final circuits


As you can understand it is a significant difference in work and cost involved and I don’t want to do it if I don’t have to. The client is a very tight as usual these days.

Thanks and best regards: Al
 
conduit is fine for earthing as long as your readings comly.
 
Hello everyone and HNY.

I need clarification on this:

I been asked to change the fuse board in commercial premises, it is a sub main SP board in a basement area. The earthing cable/cpc to board is the armor of SWA cable, all circuits to the accessories has the cpc via metal conduit. I had a look at the job and the only tests I could do is Zs. The readings where in the range of 0.40-0.50 ohms, so it seems that I have fairly good Ze and R1+R2 (still to be confirmed when the isolation can take place)

I know that for new installs, you cannot have the armor or conduit as the only means of cpc, but it is only the board change and all wiring methods complied with the regs when they were installed.


So, the question is:

· Do I have to pull a new earting cable/cpc up to the board and,
· Do I have to pull in the cpc for all wiring in the final circuits


As you can understand it is a significant difference in work and cost involved and I don’t want to do it if I don’t have to. The client is a very tight as usual these days.

Thanks and best regards: Al

Since when.. If you have proved the results comply then crack on with the board change.. Simples
 
I know that for new installs, you cannot have the armor or conduit as the only means of cpc,


You know nothing of the kind, as there is no such requirement!! Where pray tell us did you get this idea from??
 
Thanks everyone for the replies, obviously i got that wrong, i dont remember where did that came from, i did reed that somewhere, probably that was a guide or recomendation and not the regs.

I need to look in regs book more offen then.

thanks again everyone
 
Hello everyone and HNY.

the only tests I could do is Zs. The readings where in the range of 0.40-0.50 ohms, so it seems that I have fairly good Ze and R1+R2 (still to be confirmed when the isolation can take place)

/QUOTE]

You could always do an R2 as it will give a better indication of the continuity of the containment system.
 
Reg 543.2.1
" a protective conductor may consist of .............
(vi) a metal covering, for example, the sheath, screen or armouring of a cable
(vii) a metal conduit,metallic cable management system...................."
 
Thanks everyone, but from post 8 I did realised my mistake, and all relevent regs been noted. .i think this thread can remain as history now. thanks again.

Al
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

bartkusal

Arms
-
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
comercial board change
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
bartkusal,
Last reply from
bartkusal,
Replies
11
Views
1,815

Advert

Back
Top