Discuss Correct Procedure For Fault Finding On An Immersion Element in the UK Electrical Forum area at ElectriciansForums.net
I
irishsailor
Lads
Can anyone please tell me the correct procedure for fault find on an Immersion Heater Element?? Does anyone have a PDF or give me a laid down procedure
Regards Chris
Disconnect the cables. Meggar between one of the posts and earth and do a continuity test between the posts look for a reading of about 18 ohms. Usual fault is no continuity l-n as the element goes open cct. Also check that the stat is making/ breaking y twiddling the control, on a newer stat chec that the overheat stat hasn't tripped.
Its pretty straight forward really
Check That supply is going to immersion heater then safely isolate.
Check for continuity between live and neutral with a low reading ohms meter. Should read about 13 ohms. If it shows anything over 18 ohms then you know element has had it. Correct e if im wrong.
Also you need to do insulation resistence test between live and earth and neutral and earth to check you dont have a fault to earth.
isolate the circuit switch it of this should be a DP switch open the terminals at the tank put tester to ohms and as above 18-20 ohms you should get remember to measure across the heater terminals and not the heater and the thermostat.
Faults to look out for
1. faulty control stat.
2. burnt out connections at the heater due to a slack connection
3. As above at the DP switch / timeclock
4. As above at the DB
5. Faulty element heater ie open circuit or fault to earth.
6. Off peak control stat set too high that it trips out the boost control stat.(if it has a high temp trip)
7. Off peak control stat contacts welded together causing water to boil and tripping the boost control stat (if it has a high temp trip)
8. Faulty eco 7 cotroller and or no link in to allow boost function to work.
9 Ran out of ideas
Reply to Correct Procedure For Fault Finding On An Immersion Element in the UK Electrical Forum area at ElectriciansForums.net
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Hi, I have a customer with a Storad SR140-3 storage heater (in the bathroom), which does not work. The resistance of the elements is ok. There...
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Hi Absolutely 0 knowledge of this so excuse language / terms / explanation. Electric only ground floor 2 bed flat ( 3 external walls) On peak...
5K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...