B

Boberto

Can someone just give me some straight answers. Ive had a bitch of a day and i'm not thinking straight. These Kronenbourgs might have something to do with it. LOL.

With regards sub mains, on large commercial / industrial installations. When testing Zs on sub mains final circuits, if the circuits are large there is a chance the maximum Zs is exceeded. For example a ring main in a office on the third floor of a large commercial building. (I'm talking generally here, no particular job in question). If the Zs is measured as greater than the maximum Zs given in BS7671 then this doesnt comply. However with the sub mains circuits protected by a 30mA RCD there is no longer a problem because this provides additional protection? Correct?

Next scenario. Same as before but ring final circuit is not RCD protected. For example if all socket outlets are to be used for computer equipment with sockets labelled "COMPUTER ONLY" but the Zs is high still do we now have a problem? Would a resolve to this problem be to rewire the ring final in say 4.0mm as opposed to 2.5mm to reduce the Zs reading? Or drive a rod in at sub mains?

Finally earthing system at incoming mains is tncs. SWA supplying sub mains. PME cannot be exported. At sub mains a rod is installed. On Electrical Installation Cert for new ring from sub mains do we record the earthing system as tncs or tt? If a 3 core armoured taking a supply to sub mains is used should this be recorded as sub mains earthing system as tns even if mains is tt or tncs??

Just a couple of tea break discussion points from today. If im correct I stand to win a bacon sarnie tomorrow so whats the verdict !?
 
Can someone just give me some straight answers. Ive had a bitch of a day and i'm not thinking straight. These Kronenbourgs might have something to do with it. LOL.

With regards sub mains, on large commercial / industrial installations. When testing Zs on sub mains final circuits, if the circuits are large there is a chance the maximum Zs is exceeded. For example a ring main in a office on the third floor of a large commercial building. (I'm talking generally here, no particular job in question). If the Zs is measured as greater than the maximum Zs given in BS7671 then this doesnt comply. However with the sub mains circuits protected by a 30mA RCD there is no longer a problem because this provides additional protection? Correct?

Next scenario. Same as before but ring final circuit is not RCD protected. For example if all socket outlets are to be used for computer equipment with sockets labelled "COMPUTER ONLY" but the Zs is high still do we now have a problem? Would a resolve to this problem be to rewire the ring final in say 4.0mm as opposed to 2.5mm to reduce the Zs reading? Or drive a rod in at sub mains?

Finally earthing system at incoming mains is tncs. SWA supplying sub mains. PME cannot be exported. At sub mains a rod is installed. On Electrical Installation Cert for new ring from sub mains do we record the earthing system as tncs or tt? If a 3 core armoured taking a supply to sub mains is used should this be recorded as sub mains earthing system as tns even if mains is tt or tncs??

Just a couple of tea break discussion points from today. If im correct I stand to win a bacon sarnie tomorrow so whats the verdict !?


Yes, you can use the 1667 Ohm maximum, assuming 30mA RCD protection as this will satisfy disconnection times.

You can increase the conductor CSA or even use supplementary bonding to reduce Zs.

You can't export a PEN conductor but you can certainly extend PME earthing arrangements as long as bonding requirements are met, what is this distribution circuit supplying and who installed the rod?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Couple of general questions...
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Boberto,
Last reply from
IQ Electrical,
Replies
1
Views
1,220

Advert

Back
Top